Recently had a job with a wet-pipe fire sprinkler system (smaller project) that has a 6-inch double check backflow. The area static and residual pressures are pretty consistent (had a flow test of ~40 psi static and ~38 psi residual at 1,300 gpm).
We ran a forward-flow test through the backflow preventer, needing a minimum flow of about 800 gpm, which includes the hose allowances for the project (no standpipes or interior hose connections). The most flow we could get was about 450 gpm, even with three 2-1/2" hose outlets completely wide open. The static pressure following the test at the riser was about 40 psi. We used three 100 ft, 2-1/2" hoses with a 1-3/4" smooth nozzle and diffusers at the end of each hose, measuring about 3 psi pitot on each and full flow (which equates to roughly 450 gpm). Do you have any tips or advice in why we were not able to get enough flow through the backflow, or where to start to troubleshoot? Thanks in advance! Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
26 Comments
Dan Wilder
9/29/2020 08:39:45 am
First, if there are no interior hoses and if there are no hydrants between the backflow and the sprinkler system, there is no need for a hose stream allowance for this test (See NFPA 25-20' 13.7.2.1 & 12.7.2.2)
Reply
OP
9/29/2020 08:47:42 am
All good points -
Reply
Colin Lusher
10/1/2020 01:07:36 pm
Any updated OP? Curious if you've figured out where the problem is.
OP
10/1/2020 01:09:48 pm
Thanks Colin, not yet. The backflow had a specialist out and it was certified, so at this point we don't believe there's an issue with the backflow.
C.T. Carbonari
10/1/2020 02:08:37 pm
Please do post when resolved. Personally, I enjoy these MeyerFire daily posts and have learned a lot from the active community that responds to them.
Nick
9/29/2020 10:06:32 am
You need to take into account the losses through the 100' of 2.5" hose.
Reply
OP
9/29/2020 10:24:19 am
Yeah that's probably it. Maybe some elbows and playpipes right off the header would help.
Reply
Colin Lusher
9/29/2020 10:49:02 am
Agree with Dan; no need to include hose flow through backflow if there will be no hose flow going through the backflow.
Reply
Mike
9/29/2020 11:32:49 am
Isn't pitot flow pressure of the interior of the water stream flow? So hose stream friction loss is irrelevant. Pitot pressure measures the flow pressure. Friction loss of the hose would only be indicated on a pressure gauge perpendicular to the flow.
Reply
Colin Lusher
9/29/2020 12:09:48 pm
Mike,
Reply
OP
9/29/2020 12:13:38 pm
Thanks Colin - I did go back and confirm that they were 50-ft hoses and not 100-ft, but the same principles apply. I'm wondering if we can't run a 90 and playpipes right off the test header like you had mentioned.
Ramon
9/29/2020 10:43:05 pm
So, how would you put back the friction loss from the hoses?
Colin Lusher
9/30/2020 11:06:08 am
Ramon, I wouldn't recommend that. Because this is an "acceptance test", you can't really resolve the issue via theoretical calculation. Acceptance testing is meant to prove that the system functions in the real world, so if you're adjusting your results using physics theory, you're defeating the purpose of the testing.
Mike`
9/30/2020 05:02:14 pm
Agreed. Maybe a better word to use was "negligible." 450 GPM/3 hoses = 150 GPM per hose. That friction loss seems quite low and rather incapable of restricting flow enough through a 2 1/2" hose.
Colin Lusher
9/30/2020 05:34:08 pm
Mike, yes, you're right; in theory it should be pretty low, but in practice, the bigger problem I've had with flowing through a long hose is that small kinks, twists, deformations, etc. in the hose (especially at lower pressures) can really restrict the flow and increase the losses over what the theoretical calcs show.
Bob
9/29/2020 11:43:29 am
In addition to checking the tapping valve, you might check with the local water department. I sometimes ran into situations where part of the water grid was under repair or improvements affecting the system. I once ran into an issue where a water tower was down for maintenance which affected the supply a system was designed to. I also saw negative impacts from sectional valves closed due improvements in the nearby area.
Reply
C.T. Carbonari
9/29/2020 02:06:21 pm
(3) 2-1/2" Hoses should easily be able to achieve 750+ gpm flow from a 6" Underground Fireline even with a "low" pressure supply (~40 psi).
Reply
OP
9/29/2020 02:17:20 pm
It does, thank you! There is a backflow specialist that is taking a look at the backflow specifically today for any concerns/issues.
Reply
Jonathan Joseph
9/29/2020 02:12:20 pm
No need to add a hose allowance with no hose connections anywhere. I'm curious to what your sprinkler demand is at the base of the riser.
Reply
OP
9/29/2020 02:16:02 pm
Fair points; looked at running worst-case with the hose allowances since that's the way I read NFPA 13, but I see now there's mostly different opinion on that.
Reply
C.T. Carbonari
9/29/2020 03:20:18 pm
Q=29.84(Cf)(ID)^2(P)^0.5 where Cf = 0.90 ; ID = 2.55 ; P = 16
Jonathan Joseph
9/29/2020 02:40:02 pm
If you have 16 to the 1/2 power = 4
Reply
James Kyle
10/3/2020 05:51:05 pm
I have found numerous backflows with foreign debris stuck inside keeping the 2nd check from fully opening as designed. And the Backflows pass the annual test with no problem. Isn't this exactly why we are installing Forward Flow Connections.
Reply
OP
10/8/2020 12:11:36 pm
Thanks everyone for their input on this one - the verdict here was that the tap valve at the street was only partially-open.
Reply
C.T. Carbonari
10/8/2020 08:36:08 pm
I'm happy to hear that it was a minor "boo boo" with a simple fix!
Reply
11/23/2023 09:18:46 pm
It helped when you mentioned that running backflow assessments could help provide the best treatment approach. My uncle mentioned to me last night that they are planning to have a backflow preventer installed in their new home to keep their water safe from contamination. He asked if I had any idea what would be the best option to consider. Thanks to this informative backflow guide article for the best planning approach. I'll tell him it will be much better if they consult a trusted backflow testing service as they can answer all his inquiries and will provide good-quality service.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |