Is there a specific code requirement to keep the flow switch cover installed on the device?
It is good practice to keep it on, but is there a code requirement especially when running a 110V horn-strobe from the flow switch? As always thanks! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
The 2019 Edition of NFPA 1221 (Standard for the Installation, Maintenance, and Use of Emergency Services Communications Systems) Section 4.5.2 requires that communication centers "be provided with an automatic fire detection, alarm and notification system in accordance with NFPA 72."
But what constitutes "automatic fire detection?" I'm thinking this is alluding to wanting full smoke coverage of the area/space but the language of "fire detection" seems intentionally vague. A supervised automatic suppression system would meet this definition I think; its seems excessive to think a constantly attended room with fully sprinkler coverage would also require full smoke detection. Is there some other guidance I need to consider here? Is this defined elsewhere? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I have a rather basic question about fire flow . I'm a site/civil engineer working to validate a municipality's capacity for fire flow demand at a townhome development.
According to the New York State Building Code, townhomes do not required sprinkler systems. My next approach was to use the ISO Guide to determine Needed Fire Flow which is based on a few different architectural components. What I'm confused about is where is ISO used versus the NFPA 1142 standard? Are both of the standards meant to consider the large individual unit or building's area? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe We have a project with Lithium-Ion Batteries stored in racks, not to be confused with Energy Storage Systems (ESS).
This will be for an electric vehicle assembly facility. NFPA 13 to my knowledge is silent, despite some joint testing/assessment by FM Global and NFPA. The storage height of the test array was only 15-ft if memory serves which could be a significant limiting factor (link below) https://www.nfpa.org/News-and-Research/Data-research-and-tools/Hazardous-Materials/Lithium-ion-batteries-hazard-and-use-assessment My initial thought is to have a risk assessment completed by an Engineer, and have them set some design considerations based on the applicable storage parameters. I believe we're looking at single and double-row racks in excess of 15-ft in height. Has anybody else protected a similar storage array with sprinklers? Would you have any suggestions on how best to approach this hazard? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I have an existing, single-story building. It's existing Ordinary Hazard Group II that is going to change from acoustical ceiling tile throughout to have no ceiling and be open to structure. The space will essentially be wide open (like a furniture store).
The existing automatic sprinkler system has a 4 inch main that runs the length of the building with branch pipe for the sprinklers. Would it make more sense to remove and replace the branch pipe for the open structure layout with upright sprinklers, or keep the branch pipe and armover as needed for upright sprinkler spacing? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe My understanding is that when using residential concealed sprinklers in a single-family (residential) home, there is an exception to beams - that we space as if they are not present. This is in the living room (image below). I think the plan reviewer is looking for sprinklers within each bay. My reading of the code was that concealed sprinklers cannot be lowered, so I disregarded the beams. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I am working on a mixed-occupancy project using NFPA 13 (2013 Edition). The ground floor is commercial space and Levels 2-6 are residential.
The residential areas use residential-type sprinklers with two hydraulic calculations; one in a suite on Level 6 (4 sprinklers), and the other in the Level 6 Corridor. How many sprinklers should be included in the corridor calculation? Section 11.2.3.4.2 suggests it should be 7 sprinklers since they form a line down the corridor. Section 11.3.1.1 suggests that it should only be 4 sprinklers since they are residential-type. What section is correct here? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe CPVC has compatibility issues with various sealants.
As an architect, I can specify, review submittals, and keep an eye open during site visits, but there's a lot to keep track of. That goes for our engineers, who frequently cross-specify products. Throwing "compatibility" language in the spec is ultimately lazy, lame, and functionally unenforceable. Does the sprinkler industry have a way to control what comes in contact with CPVC? Is there a better way to prevent other products from being in contact with the pipe (ie: actual adherence)? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Galvanized standoff hangers are used all the time for CPVC - are they allowed to be used with steel pipe also?
Product data that I'm looking at doesn't say that they cannot be used for steel, but they say "rated for use with CPVC". If they're capable with a weaker product (CPVC), then wouldn't that be more conservative than steel? I haven't come across this before, but we have a unique structure situation where we'll be routing pipe slightly above a structural frame in a lab-type setting, and the standoffs would provide a clean/strong way to support the pipe. Thanks in advance! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I have a hospital that has two "double hose valves" at the top of two different standpipes on the roof. One is on a helipad and the other is below on a different roof. Both are the most remote locations.
Per NFPA 25, for the 5-year test, I'm supposed to flow 500 gpm at the most remote then an additional 250 gpm at a different standpipe until I reach 1,000 gpm for the fully-sprinklered building. Can I just flow 500 gpm out of both double-hose valves (2 standpipes), or do I have to flow 500 gpm, then 250 gpm, then 250 gpm using three different standpipes? Thanks. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Under the "Protection of piping against damage where subject to earthquakes" NFPA 13 requires "listed flexible pipe couplings" to be installed where pipe passes over seismic joints or building expansion joints.
Is there any similar requirement when the building is not subject to earthquakes? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Sprigs that are over 4-feet in length are required to be restrained under NFPA 13.
What options do we have to achieve this? I'd like to hear some different methods used to do this to expand my own knowledge here. Different situations like construction type and if the structural members are above or below the sprig. Thanks so much. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I have a project where we are discussing what code year of NFPA 13 will be applicable for the project.
Is the edition of NFPA 13 determined by the AHJ, the I-code year of adoption, or the state? Some of our cities spell it out, but others do not specify NFPA years of adoption, on the I-Code series. Curious to your thoughts, since this could impact exterior projection interpretation for the project. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Not all of you get to read the positive posts we receive about this Forum, but I'd like to throw a thank you out to everyone in the way of sharing some of the positive notes that have been sent in with questions. Here are a few recents:
"First - I really appreciate this forum. The discussion here are great - sometimes quick & easy and sometimes with a lot of depth. Also appreciate the variety of perspectives we each see in the same industry, so thank you." "Hello lovely forum." "Thank you for your continued FP design information it is quite helpful, especially as an independent." Now onto our Top 10 Contributors for March 2022 - thanks for all your input and expertise! Do any of your projects with dry manual standpipes hold supervisory air?
I understand NFPA 14 Section 6.1.1 to have a requirement for supervision of the standpipe system: 6.1.1 Location of Dry Standpipes. Dry standpipes shall be monitored in accordance with NFPA 72 with supervisory air pressure. Are all dry manual standpipe systems provided with supervisory air? Or is this section meant to pertain only to automatic or semi-automatic dry systems? I don't think holding supervisory air under pressure in a dry manual standpipe is feasible, being that there would be multiple points of leakage: www.aspe.org/pipeline/is-supervisory-air-monitoring-feasible-for-manual-dry-standpipes/ Just wondering if I'm completely missing the boat here, or if there's something about this portion of NFPA 14 that I'm misinterpreting. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe The state of Vermont uses NFPA 101 as their code for renovation existing buildings. There is a building with two dwelling units above a mercantile drinking establishment of less than 50 persons.
I am being told that the building occupancy is existing apartment building, but there are only two dwelling units, not three as required by definition of apartment building. Anyone have any suggestion for building occupancy and use from NFPA 101? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe We're looking at a fire protection system, Ordinary Hazard Group 2, that requires primary fire protection water from a storage tank.
We are looking at three options, (1) above ground insulated with a heater, (2) underground concrete and (3) underground fiberglass. I am curious what the community here sees around the industry as being the most common choice here? The job site already has substantial excavation going on and the job is located in the north east so freezing is a concern. There will be no private hydrant so we don't see the need to carry hose allowance in our tanks sizing. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe The NFPA 13 sections on cloud ceilings continue concentrate on sprinklers above the cloud ceilings, not the sprinklers in the clouds themselves.
If the area above the cloud is sprinklered throughout, yet there are multiple clouds greater than 4-ft wide in the shortest direction (all at the same elevation plane), creating obstructions to the sprinklers above, does each cloud obstruction need to be treated independently for sprinkler coverage beneath, or can the designer “skip” clouds or portions of the clouds and gaps, as long as the overall pendent sprinkler spacing does not exceed the maximum spacing for the hazard? I would think the opening width between the clouds would play a role in this as well, the heat's ability to skip the gap. And whether or not the sprinklers above are able to develop their spray pattern. I often see designs with sprinklers in clouds spaced out 15' x 15' leaving some clouds without sprinklers. As far as I can tell, even the 2022 edition and handbooks are silent on this. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe We have a skylight scenario that's slightly different than a prior discussion here.
NFPA 13 Section 8.5.7.1.1 states: "when a sprinkler is installed directly beneath a skylight not exceeding 32 sq.ft., the distance to the ceiling shall be measured to the plane of the ceiling as if the skylight was not present". Two things I'm not understanding here: 1) "..sprinkler installed directly beneath..": does this mean a sprinkler in the opening, somewhere in the depth of the skylight, from the finished ceiling up to the clear glass? 2) "..as if the skylight was not present." : the way I'm interpreting this is the distance from where the sprinkler is installed (the deflector) at the lower ceiling level - or we could say at the ceiling level where the skylight opening is - can be measure as if the skylight isn't there, meaning the deflector should be placed a min. 1" down from the opening, even if from the opening to the skylight glass is say 5 feet? If that is the case where a sprinkler is installed in this manner (so as to ignore the depth of the skylight), then here's one last proposal/query: a bulkhead is installed at a lower elevation than this ceiling level. So now, are we able to implement ceiling pocket requirements? The total volume of ceiling pockets is less than 1000 cu.ft. in the compartment, and with the other requirements fulfilled from 8.6.7.2, we'd be able to get away with sprinklers only in the the lower bulkhead ceiling. My issue with this though is the presence of the skylights. Hoping someone can help me out here. Thank you. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Does a diesel-powered fire pump require a full flow relief valve to prevent over pressurization due to a RPM governor failure?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe In Class I standpipes, I commonly see a pair of hose valves installed at the top landing (or intermediate landing) - One immediately below the other.
Is this an incorrect derivative of the requirement to calculate the two most remote outlets (at 500 gpm), or something that was required in a previous edition of NFPA #14, or is this merely a regional practice that is a result of the shared DNA of my regional contractors? I thought I had seen an informal interpretation regarding this, but I cannot find it again. NFPA Figures do not appear to support this double-valve arrangement. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I'm quite familiar with conducting hydrant flow tests, NFPA 291, and have read articles such at the Sprinkler Age article from Feb. 2018. And I know the residual hydrant should be between the hydrant(s) to be flowed and the large source mains for the area.
But in terms of a specific project site (especially if the underground is well-gridded), would you chose the hydrant closest to your project to be the static/residual hydrant, or would you select the flowing hydrant to be closest to your project (and adjusting the static/residual for any elevation difference)? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Under NFPA 20, Section 4.20.7.1:
The circulating relief valve shall actuate below the opening set point of the pressure relief valve to ensure cooling of the pump during churn operation. NFPA 20 Handbook: The pressure setting of the circulation relief valve should be well below the pressure relief valve setting but above the maximum suction pressure. Based on this, how do I properly specify the circulation relief valve setting that is installed on the pressure relief valve discharge line if the pressure relief valve set point is 175 psi? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe For seismic bracing, can one lateral and one longitudinal brace, attached within 2-foot of a drop to the floor below, be considered a 4-way brace?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe This isn't really a question, but I wanted to see if anyone would be willing to share drawings they have done in the past with me? I am looking to improve the look of our drawings, provide the AHJ with clear and concise information, and provide an all-around great end product. Thank you in advance! If company information, logos, location, address, etc need to be removed or blocked in order to share the drawings, I understand. Editor's note: We love this idea. If you're looking to share a sample (or set), email it to us at [email protected], and we'll update this post with images and links for discussion as they come in. Your images/drawings can be anonymous or credited, whichever you'd prefer. This could be a neat opportunity to discuss likes/improvement ideas. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe SUBMITTED DRAWINGS:
|