For hydraulic safety factors (such as in fire sprinkler systems), determining whether a 5 psi safety factor is met in a design is easy. The Available Pressure must be greater than Required Pressure + 5 PSI.
However, for percentage safety factors such as 5% or 10%, is the percentage calculated based on the Required Pressure or Available Pressure? As an example, if we have a system that requires 80 psi and the available city pressure of 88 psi, a 10% safety factor on the required pressure would be 80 psi x 10% = 8 psi safety required. In this case the minimum is met. However, a 10% safety factor on the available pressure is 88 psi x 10% = 8.8 psi safety required. In this case, the safety factor is not met. This is an extreme example, but I'm curious what others would use when looking at determining safety factors. Posted anonymously by a member for discussion. Discuss this | Submit a Question | Subscribe
10 Comments
Wayne Ammons
4/1/2019 07:34:39 am
NFPA 13 does not mandate a safety margin for hydraulic calculations. However, it is a good idea to maintain some amount of safety margin to account for fluctuations in water supply.
Reply
Scott Walter McBride
4/1/2019 10:10:40 am
I would agree with Mr. Ammons. At the end of the day it is up to the AHJ of what the requirement is and how it is to be calculated.
Reply
J Mcelvaney
4/1/2019 10:14:26 am
The City of Phoenix, AZ has the following design safety factor
Reply
Mike
4/1/2019 10:15:38 am
CBC requires 10% reduction of the available water supply flow test to be used. I use a minimum of 10% below that.
Reply
4/1/2019 10:16:47 am
From my research, there is not a specific safety factor that is required for these systems, unless there is a specific ordinance adopted by a community or you are utilizing design criteria for a specialized industry. For example, the department of energy requires a 10% or 10 psi, whichever is greater based upon their DOE-1066 standard.
Reply
RJ
4/1/2019 10:21:49 am
I have always used the following when asked for a percentage:
Reply
Dennis Clark
4/1/2019 11:16:39 am
The City of Sioux Falls requires the following:
Reply
PETE
4/1/2019 11:22:18 am
It looks like I am late to the thread, but echoing some others above: a 10% safety factor would be on the demand pressure. That is, 110% of the calculated demand pressure would have to be less than or equal to the residual pressure in the water supply at the demand flow.
Reply
4/3/2019 05:06:33 am
10 psig equired in Georgia against the available water supply. However, remember to calculate available suction pressure on the inlet flange of a fire pump based upon 150% of the rated flow at 65% available boost per NFPA 20. This suctionnpressure must not be lower than 25 psig to protect the city water supply from potential backflow conditions.
Reply
Jessica Lutz
4/3/2019 10:04:54 am
In LA County and some other areas in SoCal, they require a 10% reduction of the pressure available at the supply.
Reply