Regarding fire sprinkler system flushing of a wet-pipe gridded system; NFPA 13 Section 16.6.4 “All branch lines on gridded systems shall be arranged to facilitate flushing”.
We are doing a project which has more than 50 branches in a gridded system. Do all these branch lines need to be provided with a flushing capability? How is this commonly achieved? FM Global data sheets say to provide a small nipple between two flexible couplings, assuming removal of the nipple to flush the lines. Are there alternatives to this? Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
5 Comments
Mike
1/22/2021 09:08:07 am
I usually design tailbacks on grids and on those put a tee and plug, grooved add-a-cap, or grooved cap beyond the last head.
Reply
CJ Bonczyk
1/22/2021 11:03:25 am
A future accepted proposal from NFPA Technical committee meeting will be removing this section from NFPA 13 due to its impracticality. This will be removed from the future edition.
Reply
Fred Moore
3/22/2022 08:34:58 am
What if there was a sprinkler head adapter with a spring loaded valve that shuts off the flow when the head is removed. You would
Reply
Dan Wilder
1/22/2021 11:29:10 am
Is the flushing due to known obstructions or just to comply with the "ability" to flush?
Reply
Pete D.
1/22/2021 11:57:16 am
2 1/2" hose on the remote capped end of the float main for 15 minutes.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |