Is there any benefit to having the backflow preventer on the discharge side of the fire pump? We've seen several RFPs recently that are requiring the backflow to be on the discharge side of the fire pump.
To me it seems as though this arrangement unnecessarily leaves more pipe and mechanical components exposed to the public water supply, but I'd be interested in others' opinions. Posted anonymously by a member for discussion. Discuss this | Subscribe
13 Comments
Brian Gerdwagen FPE
2/19/2019 10:08:35 am
This seems to be a hold-over from an older version of UFC 3-600-01. The newer versions do not require this and defer to NFPA 20.
Reply
JOE MEYER
2/19/2019 10:42:02 am
Where I've seen it - it has been military requirements for the backflow to be on the discharge side, but only required on a specific project. As you've mentioned UFC 3-600-01 doesn't require this arrangement.
Reply
James
2/19/2019 10:11:59 am
From my experience, almost every water utility company will require a backflow device at the incoming service location after the house control valve. I would imagine not having one until after the fire pump be a big "no-no".
Reply
James
2/19/2019 10:14:24 am
Ah I might have misread what you asked. Is this a BFP that is additional to the one at the incoming service? I personally have never installed a BFP after a fire pump, just single check valves as per NFPA 20 diagrams.
Reply
2/19/2019 10:14:46 am
There is only one probable answer to this that I can think of.
Reply
PETE
2/19/2019 11:35:17 am
PIERRE- The backflow pressure drops are consistent with their listings. Any instantaneous cavitation that may occur on pump-run, is addressed in NFPA 20 with a 10 x suction nominal diameter distance upstream of the pump suction flange to the backflow discharge.
Reply
Franck Orset
2/19/2019 10:36:07 am
As it has been said, a check valve is necessary on the discharge side of a pump.
Reply
2/19/2019 12:40:17 pm
Backflow Prevention Assemblies (BFPA), by definition, protect the potable water supply from contaminants. Ref: Manual of Cross-Connection Control developed by the Foundation for Cross-Connection Control & Hydraulic Research.
Reply
J. Diaz
2/19/2019 03:40:00 pm
This is one of the "suggestions" from Factory Mutual. Depending on the reviewer, it could be seen as the only approved installation method. Generally, they are open and could accept the conventional way.
Reply
Ed Glynn
2/19/2019 05:48:00 pm
There is an issue where the sole source of potable water is strictly a tank that has head pressure only.
Reply
Jim
6/27/2024 08:54:51 pm
Recently ran into this same problem. Our tank pressure is not enough to open the checks on a backflow assembly engineer replaced assembly with single checks which is not an approved fix . So I’m assuming in order to function properly e would need to move our backflow to the discharge side is what I’ve been seeing
Reply
Todd Delisle
12/24/2020 10:23:03 am
NFPA does not require the installation of BFPs.
Reply
Eric
9/8/2021 05:45:04 pm
Ive read thru these comments and it makes much more sense to me to locate the backflow on the suction side of the pump. However, I have recently run across a facility with the backflow down stream of the pump. The main fire pump controller is connected between the the first check valve and the backflow preventer. The jockey pump line is connected after the backflow preventer. Heres the problem: when the first check valve fails the main fire pump continuously starts & stops because h the pressure is bleeding off they the relief valve while the jockey pump remains idle. Is this an acceptable scenario?
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |