We have a building with a double check backflow assembly on the suction side of a fire pump. Normally there is a minimum of 10 pipe diameters of vertical plane pipe just before the suction flange.
Is the double check backflow allowed within that distance? Are there requirements for the backflow to have flanges vs. grooved connections? A colleague said the control valve should be OS&Y rather than butterfly on the suction side only. Why would this be the case? I would assume the OS&Y would reduce turbulence better than a butterfly, but wouldn't the checks also cause turbulence? Thanks in advance. Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
8 Comments
Brian Gerdwagen FPE
2/1/2021 09:20:50 am
Control valves on the suction side of the pump should always be OS&Y per NFPA 20.
Reply
Jesse
2/1/2021 09:28:42 am
Backflow preventers can be on the suction side, keeping in mind OS&Y Valve requirements, etc.
Reply
Dan Wilder
2/1/2021 09:25:03 am
Well, couple of Q's and some A's for ya....
Reply
CJ Bonczyk
2/1/2021 09:37:26 am
NFPA 20 prefers BFP's/RPZ's on the discharge side of the booster pump. However many jurisdictions such as ours require the BFP on the suction side. If the device is on the suction side the following rules apply:
Reply
Mike
2/1/2021 09:51:31 am
Devices allowed in the suction piping and installation requirements are shown in section 4.15 Suction Pipe and Fittings of NFPA 20, 2016 if you have anymore questions.
Reply
Stephen L Aikey
2/1/2021 11:39:38 am
As usual there are great comments. I would like to highlight the BFP technical performance & installation data portion of this discussion.
Reply
Dale
2/8/2021 09:27:06 am
I was always instructed by my fellow well experienced Engineers to install the backflow on the suction side, as the backflow may not be listed for the now increased system pressure that the Fire Pump is providing.
Reply
2/13/2021 07:03:53 am
Thank you very much for sharing about backflow allowed before fire pump suction here… I really hope I can work on your tips and it works for me too, I am happy to come across your article. Great post I must admit, keep sharing more…
Reply