Big picture question here - I am working on an airport project. We have a Passenger Terminal Building and Aircraft Stands adjacent to the building.
I need to provide sprinkler protection with fire hose cabinets in the Passenger Terminal Building (1,000 gpm at 8 bar / 100 psi), AND fire hydrants to resupply the aircraft rescue and firefighting trucks (1,500 gpm at 6 bar / 87 psi). Do both of these demands need to be considered together to size the fire pump (both flows combined)? We are considering one duty pump and one standby pump. Thanks in advance. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
6 Comments
Casey Milhorn
3/3/2020 10:29:04 am
Typically hose demand for standpipes/hoses does not get added to fire flow demand for fire hydrants. That being said, this sounds like it might be a unique situation. What version of IFC and NFPA 14 are applicable?
Reply
3/3/2020 11:51:48 am
Most codes consider one fire scenario at a time. Therefore, select the pump for the scenario with the highest flow requirement.
Reply
Franck
3/3/2020 12:06:26 pm
As usual, the answer is « it depends ».
Reply
Mike
3/3/2020 12:34:46 pm
I've done a few projects like this in MENA. These didn't have any public water infrastructure so we ALWAYS combined the flows.
Reply
ken thackery
3/3/2020 01:12:46 pm
Some questions:
Reply
Nimal Tussa Wijetunga
3/3/2020 08:05:06 pm
You can add both together as long as if you can hydraulically prove the pressure requirement in the system does not exceed the hydrostatic test pressure of components, fixtures,fittings, material where test pressure shall be well within 200 psi or 350 psi as allowed and corresponding working pressure of 175 psi and 300 psi respectively.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |