Can a zone control valve assembly be installed downstream of another zone control valve assembly?
If there is a fire in Zone A (the primary zone), Zone A's flow switch would activate. If there is a fire in Zone B (the secondary zone), Zone A and B's flow switches would activate. Not sure whether this is permitted under NFPA 13 or 72. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
20 Comments
Pete H
8/1/2023 06:50:57 am
My personal take based on nothing:
Reply
CARLOS
8/2/2023 04:48:35 pm
But when you have to work on zone A, wouldn't that also shut off zone B? Shutting both systems down? I'm sorry but I don't agree with that set up. I believe 13 might say something against it and 25 too.
Reply
Anthony
8/1/2023 07:20:13 am
Adding to what Pete said: This happens all the time with smaller dry systems and pre-action systems off a wet system. I like to have a small butterball valve flow switch and test and drain for elevators. Kind of a mini system to keep everything isolated.
Reply
Chad
8/1/2023 07:21:34 am
As long as the controls and flows are supervised (and in the flow calcs if necessary) I cannot imagine why it would not be permitted.
Reply
Dan Wilder
8/1/2023 07:45:12 am
We do this often for individual levels of mezzanines in larger building footprints (13-22' 4.4.2, but this changes based on applicable year) and only when the primary system is wet.
Reply
Casey Milhorn
8/1/2023 08:18:01 am
I agree with everyone else and I don't know of anything not allowing it, other than than sqft limitation of NFPA 13 and your calculations. I've done it, and it has it's time and place, but as a rule I'm a fan of as few valves as possible to avoid the possibility of a closed valve (even when tampered, they get ignored sometimes). BUT, when you have trapped sections, a section prone to maintenance issues, etc, it has it's place. You just have to explain very clearly to the fire alarm guy that a signal in A means A, and a signal in A and B means just B... and program accordingly.
Reply
Glenn Berger
8/1/2023 08:24:44 am
The installation of flow series in series happens often in facilities. Easy examples are flow switches associated with elevator / elevator machine rooms and more recently with battery rooms.
Reply
Alex
8/1/2023 09:56:52 am
To echo others, yes, I believe its compliant and have done so myself before in the past.
Reply
Jesse
8/1/2023 10:21:27 am
Yep, we do this quite often. As long as both control valves are supervised and accounted for in the calculations (if relevant to the calcs), its shouldn't be a problem.
Reply
Franck
8/1/2023 02:37:03 pm
Yes, it is possible
Reply
James Evans
8/2/2023 08:36:30 am
I agree with what has been said for the most part. I do not agree with the area limitation stated in the 1st response. I believe that the area limitation is per system. If you look at this situation you have two separate systems. In this case you would have the first system acting as a bulk run for the second system. It is no different than the manifold supplying multiple risers.
Reply
Wes
8/2/2023 08:42:59 am
Oh that's a really good question. I had thought the area limitation was based upon the risk associated with having so much square footage tied to one point of failure (one valve).
Reply
James Evans
8/2/2023 09:36:21 am
I guess we need to know what they are defining as a "combined system riser" as you can see the term is singular not plural. I am not sure if one riser downstream of another riser is considered "combined" or is it considered 2 individual risers?
Wes
8/2/2023 09:47:32 am
That's a good question James. I've been so resolute on this for so long - but I'm not entirely sure.
Casey Milhorn
8/2/2023 10:28:16 am
So the area limitation conversation is always fun and lots of opinions about it. From what I understand, the sqft limitation was based on the old pipe scheduling method. The NFPA 13 Committee knew that some type of limitation was good for obvious reasons, and also practical as not to have ridiculously large pipe once you got back closer to the riser. So nothing very scientific about the limitations. I know there has been discussion about revisiting the system area limitations but I guess never a consensus on changing it, or what to change it to. I personally think keep it simple and limit it to 100,000 sqft per system no matter the hazard/occupancy type. That would equate to a lot of savings in bulk feed main, risers, and labor. NFPA 13 is still based on one fire event at a time, not multiple. I can't really think of any practical reason to limit size, other than the rare occasion of a system being down for maintenance. Of course you still have to hydraulically prove the systems and meet water delivery times on dry systems. It's definitely an interesting conversation.
Mark Harris
8/2/2023 03:10:43 pm
I agree with the comments about a single riser or control valve and the 52,000 (or less) max floor area. As NFPA 13 is written could see an issue with the added a 40,000 SF dry system since both would be out with the wet valve riser shut. But Casey brings up interesting point about the connection with old pipe schedules. Thanks for sharing that insight and may be time to up those floor area amounts.
Reply
James Evans
8/2/2023 03:39:34 pm
I still believe that each riser (or riser manifold) can start an additional 52,000sq.ft. or 40,000 sq.ft. depending on the hazard. we always have systems where a single valve turns off multiple systems or a single riser controls multiple systems since we tend to drop off dry systems and per-action systems from wet systems. No where in NFPA 13 does it state that if you do this, then you are limited to a certain square footage. We have done many maxed out wet systems with large wet systems that drop off the end of the front grid main and then goes out to a large dry system covering an exterior dock. In this scenario nothing says that the two systems must be added together and not exceed a certain area. As long as the calculations show that it works it should be allowed.
Reply
James Art, FPE, Pleasanton, Ca
8/2/2023 04:32:37 pm
Wes 8/2/2023 08:42:59 am agrees with me, so he's obviously correct! (-:
Reply
James Evans
8/2/2023 05:07:02 pm
All of this conversation is good but no one has been able to show in the code where it states that if one system such as a dry system or even another wet system drops of a primary system, that those 2 areas have to be added together and not exceed the maximum area of a single system.
Reply
WES
8/2/2023 05:31:01 pm
Did some digging on this - I wasn't 100% sure myself. The questions you're asking are really good. Sorry to be bearer of bad news. Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |