We are working on freeze protection for an enclosed canopy which is also attached to the main building. There is no exposed metal pipe to the elements.
Per the AHJ, the only approved insulating process for metal sprinkler pipe is a thermal paint insulation. I found the section for wrapped insulation that is allowed on non-metallic pipe by NFPA 13, but is there a section where wrapped insulation can be used on metal pipe? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Dan Wilder
2/17/2023 07:32:34 am
From a non-freezing part of the country....and unless the AHJ has specifically written into their adopted codes/standards this requirement, I would argue it.
Reply
Anthony
2/17/2023 07:42:41 am
Insulating pipe won't do anything to prevent pipe from freezing if there is no heat source. Insulation just slows the travel of heat it doesn't create heat.
Reply
RJ
2/17/2023 08:13:32 am
Because I said so always works with my kids.
Reply
Dan Wilder
2/17/2023 08:34:35 am
Because they don't know any better only lasts for so long...
Jesse
2/17/2023 08:04:59 am
Agree with both above comments. I would take a good look at the AHJ's local amendments. If it doesn't specifically exclude the type of insulation you want, I'd appeal it.
Reply
Glenn Berger
2/17/2023 08:11:02 am
You did not say where in the world this project is located.
Reply
Jim Derifield
2/17/2023 08:37:29 am
From my experiences in the field, when you wrap steel pipe in insulation you will also have accelerated corrosion issues over time.
Reply
Franck
2/17/2023 09:56:08 am
As indicated above, I would be very cautious with pipes exposed to freezing conditions, as water is not moving and the temperature will drop down anyway.
Reply
Schulman
2/17/2023 10:30:43 am
Heat Trace tape. Don't forget the monitoring module and the connection to the fire alarm or other monitoring/notification system which notifies maintenance that the tape has failed if it does.
Reply
Fernando
2/19/2023 12:25:20 am
And this approach is very expensive
Reply
Rob B
2/21/2023 08:06:19 am
I always love on the forums when guys are like check local amendments. This most of the times has little with solving the issue, especially in the OPS case.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |