I recently heard of an incident where the fire water return from a flow meter on a fire pump was connected low from a tank and it did not work appropriately. So as a solution they decided to connect it high on the storage tank a and somehow this configuration fixed the issue.
Both connections would have the same head due to elevation so it does not make sense to me why one would work but not the other. Why does it matter if you connect a return loop to a fire water storage tank near the top of the tank rather than near the bottom? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Pete H
7/21/2023 07:02:06 am
But doesn't the hydrostatic pressure at the bottom of the tank increase compared to the pressure at the top of the tank?
Reply
Dan Wilder
7/21/2023 08:32:31 am
The flow meter should have no issue on location of the return line. The longer line may need to be upsized due to length per 20-22' 4.22.3.4
Reply
Franck
7/21/2023 06:18:49 pm
It is probably related to the perturbations created close to the pump suction intake when water is coming back to the tank.
Reply
Jesse
7/25/2023 07:58:10 am
Its hard to see how this was an issue unless as Franck said, the return inlet caused turbulence at the pump suction.
Reply