I have a question in regards to hydraulic calculation and hose stream allowance being added to the calculations.
When and why are they added to your hydraulic calculations? Is this specifically required under NFPA 13 somewhere regardless if a standpipe is required or provided? Any insight or clarification would be greatly appreciated. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Pete H
8/2/2023 06:34:38 am
https://www.hsdl.org/?view&did=721443
Reply
Pete H
8/2/2023 07:47:19 am
Realize I never answered the "when are they added to your calculations" part of the question.
Reply
Anthony
8/2/2023 08:07:41 am
Is hose stream required by NFPA 13? Yes, NFAP 13-2016 CH 11.1.6 Hose Allowance. It is required regardless of standpipe inclusion in the building.
Reply
Dan Wilder
8/2/2023 08:10:17 am
My understanding for hose allowance
Reply
Mort
11/2/2023 02:39:57 pm
Does this mean that for a storage design you add to the sprinkler demand the 50 gpm where it connects to the sprinkler system (up to 100 gpm) and then your outside hose allowance becomes 400 gpm?
Reply
Jesse
8/2/2023 08:18:05 am
Hose allowance is indeed required by 13. It ensures that the system is designed and calculated to the anticipated water supply characteristics when the fire department is pulling water from the same system that feeds the AS system.
Reply
Glenn Berger
8/2/2023 08:24:02 am
As stated above, hose streams are required to be added to the sprinkler system hydraulic calculations. The hose allowance is added to the calculations where the fire department will connect into the system. This could be either or both a standpipe and/or nearest fire hydrant.
Reply
Adam
8/2/2023 08:53:16 am
Also to note, that hasn't been mentioned yet - When there are indoor hose stations, and the water for both sprinklers and standpipes come in on the same service line, include the indoor hose allowance volume through the incoming line up to the point where the systems branch apart from each other.
Reply
Ken
5/31/2024 11:32:07 am
It is my understanding that hose allowance is not required to be added to calculation in high rise building when a fire pump is fed from water storage tank and handling both the standpipe and sprinkler system demand. Is this correct?
Reply