According to NFPA 13 2022 Section 16.9.8.2 it is to our discretion what we consider a location " where they are not subject to mechanical damage?
When installing a Post Indicator Valve, what do you consider "not subject to mechanical damage?" Where is the line drawn, so to speak? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Jesse
3/8/2024 09:01:56 am
Placed in areas not subject to vehicular traffic. i.e. Off the parking lot / lane in a grassy area, etc.
Reply
RYAN HINSON
3/8/2024 09:51:38 am
Have you reviewed Section A.16.9.8? Since PIVs are typically used in an underground scenario and extend above grade, thus creating a potential 'target', I suggest looking at NFPA 24 (2022). NFPA 24 Section 6.3 echos NFPA 13 Section 16.9.8.2 regarding mechanical damage.
Reply
Franck
3/8/2024 10:07:06 am
Still in the prevention World and the probable events :)
Reply
J GOLDEN
3/8/2024 10:44:18 am
I will add,
Reply
Glenn Berger
3/8/2024 12:51:44 pm
Away from normal vehicular traffic.
Reply
Jack G
3/9/2024 04:28:54 pm
Please review Myer fire 1/24/2019
Reply
Todd E Wyatt
3/12/2024 08:39:13 am
The adopted scoping Code (e.g. IBC-2021) determines WHERE an automatic sprinkler system (ASPS) is required to be installed based on the building’s Occupancy Classification(s) (OC) and/or Specific Building Areas and Hazards (per IBC-2021 903.2.11).
Reply
Todd E Wyatt
3/12/2024 08:39:39 am
REFERENCES
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |