When is a fire pump pressure relief valve required?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Dan Wilder
2/7/2024 06:45:32 am
NFPA 20 - 22' (similar in previous editions)
Reply
Pete D
2/8/2024 12:43:14 pm
Just want to tag on one exception that is infrequent, but I have dealt with it. Sometimes for a very tall warehouse we size pumps to exceed sprinkler rated pressure at the discharge flange, but at the sprinkler installation elevation the pressure is at or below the rating. This is done to avoid purchasing high pressure rated sprinklers.
Reply
Pete H
2/7/2024 06:49:59 am
For pumps I'd check NFPA 20 (2016 edition) 4.19 and 4.26.5 while keeping 4.7.7.2 into account.
Reply
Glenn Berger
2/7/2024 08:11:52 am
Dan nailed the NFPA 20 requirements. One thing that I have noticed in some installations is that the additional "relief valves" do not get installed. By this I mean the casing relief valve, etc.
Reply
Dan Wilder
2/7/2024 11:11:39 am
So I ran into this on a couple jobs, if the cooling water for the pump (diesel) is pulling water from the discharge side of the impeller it acts like the casing relief.
Reply
Jack G
2/7/2024 08:18:39 am
Pressure relief valves are not permitted to relieve pressure by dumping large amounts of water.
Reply
Jesse
2/7/2024 09:23:38 am
Dan nailed it, but RayJ is also right...
Reply
franck
2/7/2024 11:29:57 am
Indicated above (including references).
Reply