For a workshop paint spray, is there a delineation for when NFPA 30B is applicable?
I am working on a maintenance shop which has a few spray paint cans. Since they are aerosols, NFPA 13 says to use NFPA 30B which has some pretty drastic requirements for design density. Yes, the easy answer is a flammable storage locker, but has anyone ever had to design to the full requirements just by the mere presence of paint spray cans? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Glenn Berger
2/27/2023 08:12:10 am
The mere presence of paint spray cans, unless there a quantity presence, does not trigger NFPA 30B requirements. With that said, your question did not give specifics of the application that is being asked. Flammable lockers would be a good start in commercial applications.
Reply
Todd E Wyatt
2/27/2023 08:19:43 am
SUMMARY
Reply
Jesse
2/27/2023 09:02:01 am
Having paint spray cans or other Level 3 aerosols on site doesn't necessarily trigger 30B as the governing standard, and a listed flammable liquid / aerosol storage cabinet may suffice. What kind of quantities are we talking?
Reply
Anthony
2/27/2023 09:25:59 am
This is one of my personal favorites when NFPA 13 directs you to another NFPA standard that redirects you back to NFPA 13.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |