I don't deal with storage in fire protection systems - but I have a question regarding different storage arrangements.
When does a system have to have in-rack sprinklers? Are there always alternative solutions that an owner can use to avoid in-rack sprinklers? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Pete H
12/10/2021 06:51:37 am
In chapters 16 and 17 (protection of rack storage of class I through class IV commodities, and protection of rack storage of plastic commodities, NFPA 13 2016 edition respectively), there are charts that show you storage arrangements that may require in rack sprinklers depending on storage heights, encapsulation, and aisle width.
Reply
Alex
12/10/2021 06:51:48 am
Hi,
Reply
Dan Wilder
12/10/2021 07:27:55 am
Without sounding too condescending....when the NFPA charts require them based on commodity, storage height, encapsulation, aisle width, pallet type......
Reply
Jesse
12/10/2021 08:14:33 am
Not nearly enough time and space to answer this.
Reply
Vince Diorio
12/10/2021 08:14:47 am
I do high pile storage design throughout the country. NFPA 13 Chapters 12 forward to 21, IFC Chapter 32, FM many chapters is use everyday along with discussions with the AHJ an the clients insurance company. There are many ways to get the roof fire sprinkler system to handle high pile storage depending on the type of commodity that's being storage. Definitely way to much to type. So many new fire sprinkler heads that are out now for this type of fire protection.
Reply
Franck
12/10/2021 08:43:40 am
Almost everything has been said. Too many possible answer to the same question (When does a system have to have in-rack sprinklers?) depending on storage configuration, height, ceiling density, type of sprinkler, etc.
Reply
Sundance
12/10/2021 09:53:00 am
Expanding on Franck’s comment related to solid shelving. This has been a major issue for us and NFPA-13 (2019) really doubles down on how a “solid shelving” condition created by the “placement of loads” with a footprint greater than 20 sf even to the point of putting bare steel pipe on cantilever racks, etc. I see several comments above referencing NFPA-16 and this “solid shelf” requirement is already expressed in that version as well.
Reply
Glenn Berger
12/10/2021 10:34:20 am
Concur with the above comments. I try to avoid in-rack sprinklers at all cost!
Reply
Ivonn
12/10/2021 10:37:54 am
Are there always alternative solutions that an owner can use to avoid in-rack sprinklers?
Reply
sean
12/11/2021 07:59:45 am
A general rule of thumb is a basic heads has much less storage it can protect without in-rack and your allowed more and more as you approach ESFR.
Reply
Sundance
12/11/2021 10:04:05 am
Related to “solid shelving” whether created with shelf material or by the “placement of loads” >20 sf, once you go over 12’ in height in a Storage Occupancy (there are some special provision under Mercantile Occupancy), to our knowledge, there is no way around In-Racks. This provision is not dependent on the “Roof Level System” type and it does not matter if you have ESFR, K-25, etc.
Reply
sean
12/13/2021 08:15:13 pm
this is really interesting. Ill have to look into it as applies to 2021 IBC
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |