When doing a flow test for a 5-year on an automatic wet standpipe system in a building which has had significant additions over the years, which design pressure applies?
The original 8-story building and pump are from the early 1980's and was required to have a minimum residual 65-psi at the roof, flowing 750 gpm. Fast forward to the most recent building attachment to the existing fire pump, and the code now requires a minimum of 100-psi at 750 gpm at the roof. Would these additions be considered separate zones and therefore be tested individually at their specific design requirement, or would they all be tested at the original design requirements? The building is a healthcare facility and is inspected to NFPA 25-2011 per the Joint Commission requirements. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Alex
12/7/2021 08:08:57 am
Hi,
Reply
Glenn Berger
12/7/2021 08:13:46 am
Concur with the response provided by Alex above.
Reply
Anthony
12/7/2021 08:19:19 am
Systems are tested to see if they operate as designed.
Reply
RJ
12/7/2021 09:44:44 am
In the state of Illinois, it doesn't matter what the codes say, it only matters what Joint Commision and IL Department of Public Health says, concerning nursing homes and hospitals. (Unless you are lucky enough to talk them into seeing it your way.)
Reply
sean
12/31/2021 06:36:09 pm
you still have to follow local laws IFC etc.
Reply
Jay
12/9/2021 07:44:57 am
2011 NFPA 25 requires the standpipe to be tested at the pressure and flow of its original design and installation. I would consider these to be different zones for testing purposes.
Reply
sean
12/9/2021 01:19:42 pm
I would see the latest drawings, if those include provide calcs to the existing areas at 100 psi that applies everywhere if no new design cals were done for the existing they only need to meet the original design of 65 psi
Reply