NFPA 13 provides allowed omissions for sprinklers in combustible concealed spaces where the entire cavity is filled "with non-combustible insulation".
Is fiberglass the only non-combustible insulation? Is blown-in insulation considered to be non-combustible, or does it depend on the type of blown-in? Just curious if there was helpful literature so that we knew what to recommend or look for when we come across these scenarios. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Dan Wilder
6/23/2021 08:05:24 am
Fiberglass & Mineral/Rock Wool type insulation is the "go to" for non-combustible insulation.
Reply
schulman
6/23/2021 08:20:42 am
as long as it complies with / is listed as complying with ASTM E84 you should be good ...
Reply
Franck
6/23/2021 08:32:26 am
You may also look for a possible "FM approval" for your insulation.
Reply
Todd Wyatt
6/23/2021 09:08:14 am
Depending on the applicable Building Code (and/or other AHJ requirements) for the Project, the definition of what is "noncombustible" may vary.
Reply
Justin Milne
6/23/2021 11:51:28 am
The comment in the NFPA 13 code reference states, "concealed spaces of noncombustible and limited-combustible construction with minimal combustible loading having no access shall not require sprinkler protection."
Reply
John Galante
6/29/2021 04:10:48 pm
Review “ flame spread” requirements of the 13 code.
Reply
7/23/2021 01:17:15 am
Good content. From your content, I have got more information. Thanks for your content and I hope you will give this type of content in the future.
Reply
10/16/2022 04:36:15 am
What is an XPS board?
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |