How does NFPA define a "Revamp"?
In NFPA 13 2019, Section 29.5.2 states that "Calculations shall be provided to verify that the system design flow rate will be achieved" when revamping a hydraulically designed system. The problem me and my coworkers are having is that we cant agree on a definition of "Revamp" and NFPA does not seem to define it either. One opinion is that any "modification" constitutes revamping, and so any sort of modification will require calculations. Another opinion is that any sort of new addition to a system or hazard change requires calculations. We have almost always defaulted to just calc it and leave it be, but would love a more defined definition on when calcs are needed. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Pete H
6/21/2024 06:40:32 am
No actual authority behind this, not even double checking books to see if I can verify, just taking a shot in the dark:
Reply
Scott McBride
6/21/2024 08:19:34 am
When it comes to NFPA or ICC if the definition is not within the document itself then the definition is to be common meaning from the dictionary, such as webster's.
Reply
JI
6/21/2024 09:26:02 am
I agree to all of those points. The addition of a backflow preventer of some sort is another item that comes to mind.
Reply
Dan Wilder
6/21/2024 08:15:23 am
Well, Chapter 3 has definitions and also states where a term is not defined "...they shall be defined using their ordinarily accepted meanings within the context in which they are used. Merriam-Webster's Collegiate Dictionary 11th Edition, shall be the source for the ordinarily accepted meaning."
Reply
Glenn Berger
6/21/2024 08:26:55 am
Sounds like judicial (lawyer) speak to me because of a previous definition interpretation.
Reply
Jesse
6/21/2024 10:02:26 am
I want to reiterate a couple comments related to definitions and a dictionary.
Reply
Troy N
6/21/2024 10:33:21 am
Great question,
Reply
Chris Heyer
6/21/2024 10:58:01 am
I would take it on a case by case basis, but definitely if changes were made beyond the most hydraulically demanding area
Reply
Jack G
6/21/2024 12:17:09 pm
Good points and I agree.