We have a project where we're using a vertical turbine fire pump.
NFPA 20 makes reference to a 'water level' at 150% of pump rated capacity. What exactly does this 'water level' mean? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Alex
11/24/2021 05:33:50 am
Water level refers to your usable water supply. For example, if you have a tank located 100 feet away from your building, you are going to battle friction loss through the pipe, meaning once you get down to the final few feet of water in your tank, there won’t be enough pressure to drive the water to the pump.
Reply
Franck Orset
11/24/2021 10:22:39 am
Alex, this is true for horizontal fire pumps taking suction from a tank, but the question is for a vertical turbine fire pump, where there is no pipe between the tank and the pump with friction loss.
Reply
Jesse
11/24/2021 09:54:55 am
I started to respond. Then had to refresh my screen and saw the Alex had already done so, and covered it all. Nothing to add to Alex's response. J
Reply
Jack G
11/24/2021 10:00:15 am
From memory, 20 states the required submerge certificate “ shall be obtained from the manufacturer”, somewhere, Chet 7. ( wet pits)
Reply
Franck
11/24/2021 10:30:02 am
You may refer to pump submergence with well installations.
Reply