Hi All, I have a two part question regarding sprinklers below ductwork exceeding 48" wide. Both areas below (in different locations) are Ordinary Hazard, 130 sqft maximum spacing. When protecting below the ductwork in the elevation sketch below, is the 6'-11" dimension doubled to be 13'-10" the same as when spacing to a wall (SxL) ? Or can the distance to the next sprinkler be 15-ft (15 x 6-11 = 103.75 sqft)? In the plan view below, are sprinklers required below the 60" wide duct ABOVE the AHU (shown in green), if the vertical distance between the AHU and bottom of duct is greater than 24"? This would be under NFPA 13-2019, Section 9.5.5.3.1.5. Many thanks!
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Glenn Berger
4/23/2024 08:13:42 am
Sprinkler below duct are there to protect the space below the obstruction only. The distance to the end wall is not applicable IN THIS CASE, since there is a significant distance from the wall.
Reply
Jesse
4/23/2024 08:36:11 am
Pretty much what Glenn said. In OH1 and OH2 you can have 15' sprinkler spacing as long as sprinkler coverage doesn't exceed 130- sq. ft.
Reply
Justin
4/23/2024 09:47:16 am
Thats what I thought too but NFPA 13 allows it as long as the head is no further than 3inches from the outside edge and the sprinkler has a water guard to protect from activated sprinklers from above. Specifically Code requires an intermediate rack type which is the same as a multi level sprinkler noted in the elevation view. However it would be nice to see some test data back up the 3 in allowance claim.
Reply
Pete H
4/23/2024 08:50:24 am
Echoing Glenn and Jesse, you can go up to 15'-0" apart. The double to the wall measurement doesn't apply because you have protection on either side of the obstruction and there isn't actually a wall stopping spray. You are just protecting underneath the obstruction with this sprinkler.
Reply
KC
4/23/2024 09:27:46 am
As a follow up to my original post - I have always failed to see how a sprinkler head below a duct will "collect" heat without a draft stop but have always designed that way until recently - that said - I have started using NFPA #13 (2019) section 9.5.5.3.1.2 (see the figure) - This allow sprinklers to be adjacent to the duct rather than beneath it. As to the 2nd part of my question - I believe that sprinklers will be required either adjacent to or below the duct if the vertical distance to the top of the AHU to bottom of duct exceeds 24"
Reply
Paul
4/23/2024 09:32:09 am
I am not in total agreement with the above responses, the edge of your duct work would be treated as a wall. You are doubling that distance as the sprinkler is going to discharge to cover that area and in other directions (e.g. 6.917 ft. x2=13.834 ft. resulting in a max spacing of 9.397 ft. between sprinklers for a maximum 130 sq. ft. coverage area and a water delivery of 19.5 gpm minimum)
Reply
Dan Wilder
4/23/2024 10:00:14 am
Ductwork, that is the half distance between the sprinkler and the edge of duct (as if there was a wall on the far side) so that distance x2 so the max distance along the duct should not exceed ~9'-4" on center (130ft² / (6'-11" x 2)) = 9'-4". The sprinkler is expected to spray that far so under any other circumstance, it would be the half distance.
Reply
Casey Milhorn
4/23/2024 10:17:18 am
I might be in the minority here, but I think this is a case of overthinking it. The fact that you have a head installed there at all is 90% of the battle. Worrying about discharge, calculations, etc... for an obstruction level head is majoring on the minors as one of my mentors would say. If you are worried about it, use a vertical sidewall which I know would be limited to 10x10 in this scenario, but would make a lot more sense in a practical way. At the end of the day, IF this head were to active first, which it probably won't, then great job, it is helping control a fire in it's early stages. If it doesn't active first, it probably won't active at all due to heat collection and cooling/suppression by ceiling level heads.
Reply
Jack G
4/23/2024 03:59:51 pm
If there is protection on both sides of the obstruction ( 1/2 x on each side) then protection beneath the duct is for under the duct.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |