Is there support in the standard to require a control valve supplying a combination sprinkler/standpipe system (standpipe isolation valve) so that a ladder wouldn't be needed to close the valve?
All control valves are to be accessible, but not necessarily readily accessible. I like to require that they not be installed more than 7-ft, but am looking for code guidance here. Is there code justification for 7-ft valve requirement? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
Alex
11/9/2022 05:14:24 am
Hi,
Reply
Todd E Wyatt
11/9/2022 08:27:07 am
2021 NFPA 13 :
Reply
Franck
11/9/2022 10:59:53 am
As indicated above, this is a requirement to be accessible and the 7 ft is an indication (that's why it is in the annex section).
Reply