Can window sprinklers be used to protect internal glazing in partitions in lieu of fire rated glass partition?
The life safety engineer has requested to provide sprinklers on internal fully glazed partitions to save the cost of fire rated glazed partition. Not for the entire hospital, only some internal partitions in a hospital for glazing with 1-hour fire rated ones. Although couldn't find anything in the NFPA 13 that support his request as I know this is valid only for atriums, am I right? I appreciate the help and response as always. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Anthony
5/8/2024 08:17:59 am
Window sprinklers and wall ratings are available in NFPA 12- 2016 see 8.15.26.
Reply
Jack Smeck
5/8/2024 08:42:15 am
Hi there,
Reply
Todd E Wyatt
5/8/2024 08:43:35 am
Per the scoping Code (e.g. IBC-2021) there are (3) methods for determining the fire-resistance rating (FRR) of building elements, components or assemblies including FRR glazing :
Reply
Todd E Wyatt
5/8/2024 08:44:02 am
REFERENCES
Reply
Glenn Berger
5/8/2024 08:59:33 am
This is definitely accepted practice. You might be able to find some documentation in openings in rated construction and similar discussions.
Reply
Steve Cooper
5/8/2024 09:20:26 am
Check out ESR-2397. It is an evaluation report for two Tyco window sprinklers. Goes over how and when to use them. It also sites all the codes it is compliant with. It has the hydraulic requirements as well.
Reply
Jerry Clark
5/8/2024 09:26:44 am
Yes, you can. Now allowed in various applications, not just atriums. We employed this method of protection in 2-hour egress corridors for a large Google project:
Reply
Brett
5/8/2024 09:58:44 am
Yes, you may use sprinklers to protect glass (glazing). There are a few companies who make window sprinklers. You will also find standard sprinklers used in older installations. There is also a Meyer Fire post on this: https://www.meyerfire.com/blog/windows-sprinklers-fire-ratings-part-i
Reply
Dave
5/8/2024 10:42:23 am
Reliable has a good, archived webcast from Dec. 2020
Reply
Franck
5/8/2024 12:54:08 pm
I would say yes if the windows are there and you need 1h rating.
Reply
cathy
5/9/2024 10:48:33 pm
1, TYCO TY3388 window sprikler.
Reply