Can I use the small room rule out of NFPA 13 in an office with varying ceiling heights?
The room has a partial 8'-0" ceiling and a partial 8'-6" ceiling with the vertical section closed in. We're under NFPA 13-2016. The sprinklers meet the obstruction rules out of Chapter 8 and the spray pattern develops to protect the entire floor space without being obstructed by the change in ceiling elevation. Based on the definitions below, it looks like the ceiling doesn't need to be flat, but I want to make sure I'm applying the rule correctly and I can use a 9'-0" dimension for the small room rule in this situation. NFPA 13-2016 Section A3.3.2.2 defines a small room rule as a compartment of light hazard occupancy classification having unobstructed construction and a floor area not exceeding 800 sqft. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Pete H
11/5/2021 06:54:20 am
Long as you don't have an unprotected ceiling pocket as allowed by 8.6.7 and 8.8.7 exceeding 32 square feet and there's no unprotected area above a cloud ceiling (doesn't sound like you have a cloud ceiling anyway), sounds good (in my opinion).
Reply
Pete H
11/5/2021 06:55:24 am
Er, ignore this comment, this is the extra rules for design area reduction.
Reply
Alex
11/5/2021 07:08:18 am
Hi,
Reply
Glenn Berger
11/5/2021 08:26:32 am
You are correct in your interpretation of the small room rule.
Reply
SCHULMAN
11/5/2021 08:39:53 am
JUST LEARNING THIS STUFF,
Reply
Franck
11/5/2021 10:45:43 am
8.6.4.1.1.3 regulates how you will install sprinklers when you have some possible obstructions to the sprinkler pattern discharge (that would prevent a correct wetting of all areas located on the ground floor).
Reply
CJ
11/5/2021 08:57:33 am
This is an acceptable means of protection and the small room rule for sprinkler layout does apply in this situation.
Reply
Jesse
11/5/2021 11:31:23 am
Yep, small room rule can apply here
Reply