Is there anything in NFPA 13, 2019 that allows us to use Table 4.3.1.7.1 Discharge Criteria for Miscellaneous Storage Up to 12 ft in Height for Rack Storage of Class I Through Class IV Commodities Stored Up to 12 ft in Height?
NFPA 13, 2016 §16.2.1.2 Protection Criteria for Rack Storage of Class I Through Class IV Commodities Stored Up to 12 ft in Height sends us to Table 13.2.1 for protection criteria (the same as miscellaneous storage). The 2016-2019 Roadmap provided in NFPA 13, 2019 shows §16.2.1.2 (and the associated sections) as deleted. NFPA 13, 2019 §21.4.1 provides protection criteria for Rack Storage of Class I Through Class IV Commodities Stored Over 12 ft Up to and Including 25 ft in Height and §21.4.2 provides protection criteria for Rack Storage of Class I Through Class IV Commodities Stored Over 25 ft in Height, but there is no protection criteria provided in NFPA 13, 2019 Chapter 21 for Rack Storage of Class I Through Class IV Commodities Stored Up to 12 ft in Height. Thanks in advance! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Brett
6/27/2024 06:57:25 am
Section 20.1.1.
Reply
Glenn Berger
6/27/2024 08:16:45 am
I may not be understanding your question correctly.
Reply
Dan Wilder
6/27/2024 08:33:33 am
You would first need to define the storage as either Miscellaneous Storage or Low-Piled Storage (it's not one big pot anymore and they removed the chart). The big defining factors would be:
Reply
Jesse
6/27/2024 09:06:39 am
Misc. Storage and Low-piled Storge used to pretty much be the same thing. Insurance companies often referred to it as "incidental storage", basically storage that was incidental to the occupancy.
Reply
Casey Milhorn
6/27/2024 09:35:21 am
What Dan said. Not the same thing and you will need to meet the definition of one or the other.
Reply
Pete H
6/27/2024 01:21:40 pm
Sounds like it's low-piled storage.
Reply
Jack G
6/28/2024 11:47:17 am
Be careful of the allowable spacing for your densities for low piled, high piled and misc storage. In the Meyer fire tool kit there is an excellent cheat sheet for “ sprinkler spacing “.