Does anyone know of a UL Listed 1-inch Solenoid valve?
And now to make it harder, the AHJ is specifically calling for this solenoid listing to be for "Fire Sprinkler" not just "Fire Protection" or even "Fire Suppression". They wish to require a normally-open solenoid valve (approved and listed for fire sprinkler use) for the sprinkler at the top of an elevator shaft and we're trying to work with them. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Alex
8/26/2022 06:11:03 am
Hi,
Reply
M. Newell
8/26/2022 09:25:12 am
If you go UL Product IQ, https://productiq.ulprospector.com/
Reply
Jesse
8/26/2022 10:31:20 am
I got nothing. That's a weird one.
Reply
Dave
8/26/2022 11:01:27 am
A delicate situation, this is usually where I reach out to my technical services of the manufacturer I utilize (e.g., Victaulic, Reliable) for relief. This is an interesting article on UL / FM from the QRFS blog.
Reply
Glenn Berger
8/26/2022 11:52:43 am
Not familiar with any general UL/FM approvals for solenoid valves. Only seen approvals with deluge valves, clean agent systems, etc.
Reply
Sophia
8/26/2022 01:14:52 pm
We had the exact same request from AHJ to provide them a UL Listed 1-inch Solenoid Valve (a normally open solenoid valve, approved and listed for fire sprinkler use) for the Elevator Shaft in Self-Storage Project back in 2015.
Reply
Thomas Duross
8/27/2022 12:56:25 pm
Have you looked at Jim McHugh's remote test?