We are designing a warehouse which has a system demand of about 150 psi at 2,000 gpm.
There is an existing facility with a 150 psi @ 1,000 gpm rated pump installed approximately 1/4-mile (350 m) from the warehouse. We are planning to add a new 150 psi pump at 1,000 gpm near the warehouse roughly 65-feet (20 m) from it. Is there any code limitation we might hit to serve one building with two separate pumping stations installed remote from each other? How would you recommend we set the pump operation sequence for the two pump rooms? Each pump room will have an electric, diesel, and jockey pump. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Dan Wilder
6/7/2021 08:19:12 am
Couple questions:
Reply
Casey Milhorn
6/7/2021 09:12:40 am
Same questions as Dan. Will the pumps be in parallel and at what point do the supplies join back together? I would definitely involve a good local pump rep that has done this type of setup before. This is similar to a redundant pump setup for high-rises. It may take the better part of a day playing around with the pressures until you get it right.
Reply
CJ Bonczyk
6/7/2021 09:23:00 am
I concur with Dan there is a bit more information that is needed in order to give you a more definitive answer. I would also strongly suggest contacting the local AHJ and advise them of the situation as they may have local requirements that do or do not allow this setup as the location and accesses are required to be preplanned with the fire department per NFPA 20 § 4.14.1.1.4 & 4.14.2.1
Reply
Franck
6/7/2021 10:45:15 am
It is not uncommon to have fire pumps set up as 2 separate water supplies.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |