We had a tip last week about being able to comment and share ideas from our articles on the Blog and our hits series - and we love the idea. The hope is to open a thread once-a-week concerning the Blog topics so we can expand and discuss in greater detail. My hope is that this doesn't take away from the Forum at all (again, just once a week), but allows opportunity for further discussion where it's wanted. This thread is for Components of a Fire Sprinkler, with our high-quality image above (right-click to download and save).
Thanks everyone! - Joe
11 Comments
Pete A
8/9/2023 12:09:32 pm
I was always under the impression that the orifice is the actual opening the plug seals in to. The larger the K-factor, the larger the opening. Nearly all the sprinklers I deal with have 1/2" NPT threads, but they have varying K-factors (up to 5.6) - meaning the plug opening varies. This picture, and all I found with a quick search, show the orifice at the threads, not the plug. Am I missing something?
Reply
Joe Meyer
8/9/2023 12:12:57 pm
Thanks Pete! I think you're right - I've tried to show the orifice as the actual opening (the most-constricted portion of the opening), but had trouble illustrating that concept. The orifice is the inside diameter so-to-speak, not at the threads, yep.
Reply
8/9/2023 12:13:25 pm
Though it is not a component, it would be very useful to show where the sprinkler ID #, UL/FM marking to look for on the sprinkler deflector.
Reply
James Art, FPE
8/9/2023 12:54:41 pm
NO!
Reply
Joe Meyer
8/9/2023 01:56:16 pm
Thanks James! I appreciate the input - hard to show on this image but you've nailed it. I appreciate it!
Reply
Adam
8/9/2023 01:43:09 pm
In your newsletter, you list the correlation between K-factor and orifice size (pasted below). I had been looking for this information a while ago, and I thought it would be readily available, but had no luck finding anything.
Reply
Joe Meyer
8/9/2023 01:55:18 pm
Thanks Adam! I wrote it down myself to matchup inspector's tests sizes for stocklisting - but I don't recall the source.
Reply
Joe Meyer
8/10/2023 07:42:32 am
Big thanks to Dan Wilder - who emailed a few references.
Reply
JI
8/10/2023 08:54:54 am
Not all sprinklers have threads on them. Victaulic uses grooved sprinklers in 1/2", 3/4", and 1" sized grooves, which attach to a grooved sprinkler outlet using a Style V9 Coupling as a part of the IGS system.
Reply
Hello, I have been looking at the table for Nominal Orifice Size in Table A.7.2.2.1 of NFPA 13, 2022 Edition. What I find surprising and also confusing is that the orifice opening for K5.6 and for K.8.0 can be the same = 13 mm but still different when in 'inches' (1/2" and 17/32")? Can anybody explain ?
Reply