I'm looking at a building that is a convent home (residential) but has a chapel, bedrooms, dining room, kitchen area and a few mechanical support spaces.
I would think the building would be classified as light hazard because that is what a majority of the building is. But some could argue that some of these spaces are Ordinary Hazard 1. Should the tank be sized on the Ordinary Hazard 1 demand or the Light Hazard demand? Thanks for you help, Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Dan Wilder
6/6/2024 07:12:20 am
What is the official building occupancy as designated by the Architect? that will provide the needed information and also what is considered ancillary to the main occupancy.
Reply
Pete H
6/6/2024 07:59:50 am
Completely agree with Dan, just posting to reinforce that a larger kitchen can push you into ordinary. And I could see that actually being a decent size if they try to cook for the nuns en masse.
Reply
Jesse
6/6/2024 08:06:54 am
While the majority is Light Hazard, you do have some OH1 areas that will drive your density for AS as well as well as your tank size. You'll need to size your tank for the greatest demand.
Reply
Mike Morey
6/6/2024 08:12:17 am
Is it 13 or 13R? 13R if the rooms are 500 sq ft or less you can limit the demand to a 4 head calc even for OH. If 13 or over 500 sq ft you may still be able to limit the volume using the QR reduction etc. In that case arguably you'd still have to provide the "phantom flow" to reach whatever the minimum design area you can squeeze down to is x density even if you don't have to calculate that many sprinklers. Also unless you're providing hydrants or hose valves you can throw out the hose flow. Lastly, assuming there's a reasonably good refill source you may be able to size it down using the break tank rules if you provide the appropriate automatic refill apparatus.
Reply
Glenn Berger
6/6/2024 08:16:07 am
Completely agree with Jesse.
Reply
Franck
6/6/2024 08:26:05 am
Fully agree with Jesse & Glenn
Reply
Anthony
6/6/2024 08:27:00 am
I also agree with those indicating the tank shall be sized to the greatest demand.
Reply
Jack G
6/6/2024 10:55:30 am
In agreement.
Reply
David C
6/6/2024 07:22:45 pm
The A occupancy(Assembly) is the highest order of concern here in my eyes, as referenced earlier. (Yes a full code review including separation walls between mechanical and storage are the normal order of things)
Reply