I'm working on a performing arts theater in California. There are floating clouds with pendents in them.
I seem to remember an inspector bringing up an NFPA requirement for either a swing joint or a flexible drop to connect to the pendent sprinkler. I can't find anything in the 2016 Edition of NFPA 13. Is there a requirement for a swing joint or flexible drop for a cloud? Could anyone provide a code reference? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Glenn Berger
2/28/2023 08:06:02 am
Recommend approved flexible hoses to be used to pipe to sprinklers in the floating (suspended) clouds.
Reply
Anthony
2/28/2023 08:19:43 am
First off get the code excerpt whenever someone says there is a requirement you've never heard of. 9/10 times they mean "old Jimmy Fitterwise always said" the other 1/10 times you learn something.
Reply
Anthony
2/28/2023 08:51:45 am
Per some of the comments here I think perhaps the fitter is referring to 9.3.2.4
Reply
Jess Lutz
2/28/2023 11:16:20 am
Hey, that "old Jimmy Fitterwise" has had some good information! LOL.
Reply
Anthony
2/28/2023 12:42:58 pm
Today was a learning day :)
Glenn Warga
2/28/2023 08:29:09 am
This is most likely coming from the seismic section where you either have to have an oversize hole or on flex drop. The oversize hole may not be practical when dealing with concealed heads or some other type of decorative environment.
Reply
Ken Thackery
2/28/2023 10:44:06 am
Glenn,
Reply
Ken Thackery
2/28/2023 10:59:33 am
© NORTHWEST WALL AND CEILING BUREAU
Dan Wilder
2/28/2023 09:24:20 am
Nothing within NFPA specifically, this falls over to the IBC/ICC for requirements which transition back into Chapter 9, however there may be local amendments concerning different parts of the building moving independently of each other that would require some sort of separation/movement via flex hoses (seems a little too specific of a requirement). Flex hoses are not listed for a seismic separation application (think Metraflex), only to remove the oversized hole requirement for the penetration within the ceiling to avoid damage to the sprinkler from impact to the ceiling.
Reply