A project has restroom stall walls that run floor to ceiling. There are gaps above and below the door for venting. Are strobes required in each stall? Audibility would be provided with a combination horn/strobe in the main restrooms space.
Note: This is a Daily Discussion question submitted anonymously to us. Submit a Question or Discuss This Here.
3 Comments
Joe Meyer
11/2/2017 06:25:18 am
With walls floor-to-ceiling, there likely isn't much visual notification within the stalls themselves. Being that the stalls are often publicly accessible, visual notification should still be required by NFPA 72.
Reply
Kyle MacKenzie
1/7/2022 08:08:31 am
3 thoughts regarding your comment Joe:
Reply
Jason Lupa, PE
2/15/2022 08:44:59 am
For strobes, NFPA 72 describes two methods of visible signaling: direct and indirect. Both of these methods are designed to notify building occupants of an emergency condition by a direct viewing of the visible appliance or by illuminating the surrounding area.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |