I’ve been reviewing standards to determine the equivalency between fireproofing thickness and the fire resistance rating.
This is for an industrial plant structure. I realize there are many factors but at some point I need a reference to determine what the rating is required to be. What is the process to determine what the required fire-resistance-rating of a component needs to be? In this case, it is for structural steel supporting columns of the open structure. The structure is composed of the main support columns and those supporting vessels, etc. The structure is about 5-6 levels tall. For simplicity I wanted to address the main columns starting on floor 1 where a pool fire may start. If I could find the standard / guidance for this then I can adapt for vessel supports, etc. I’ve been through calculations and information from API 2218 to determine the fireproofing thickness for a certain hour rating. However, I have yet to determine or find the hourly rating requirement. I’m assuming it will be 1-3 hours, for example, using API 2510 (LPG) as a guide with reference to UL 1709. It does specify a 1½ hour time rating which then gives a fireproofing thickness. Further, the fire protection requirements will come from a risk assessment of the system. I have to be able to give guidance to the risk team to help them come to suitable answers. What can I use to provide a best answer to an hourly rating, hopefully, chapter and verse? Thank you for your help in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
James Stever Jr
1/13/2023 09:30:23 am
Check your applicable building code to find the code required rating and the reference standards applicable to the building code. Also check UL
Reply
Todd E Wyatt
1/13/2023 09:50:30 am
The Design Professional (e.g. Architect, Engineer) determines the Type of Construction (TC) of the Project based on the applicable Code(s) (e.g. 2021 IBC, 2021 NFPA 101 Life Safety Code).
Reply
Chuck Riforgiate
1/13/2023 10:41:27 am
The International Building Code in Section 722 provides a prescriptive method to calculate fire resistance ratings of materials and assemblies. This section also contains provisions that would permit modifications or changes to a tested assembly. Section 722 includes methods for calculating fire resistance for seven different construction materials: concrete assemblies, concrete masonry, clay brick & tile masonry, steel assemblies, beams, trusses and wood assemblies.
Reply
Ryan Hinson
1/13/2023 10:45:37 am
Does your client have their own design guidelines? Many do.
Reply
6/17/2023 02:53:57 am
How Can I Tell If Something Is Fireproof? a lot of queries are brought up concerning how to calculate the needed fire resistance rating for components in a manufacturing plant. In order to determine the appropriate thickness of fireproofing for structural steel supporting columns, the author requests recommendations for relevant standards and reference materials. Reviewers applaud the author's research on API 2218, however they note how difficult it is to pin down the precise hourly rating required. It would be helpful if the article expanded on some points or linked to related material. However, the review provides a good place to begin for experts seeking information on how to evaluate buildings for their fire safety. Many people, in the future, will read this, I have no doubt.
Reply