Do open (exterior) stairs need standpipes?
If the stairs are more than 50% open, sprinkler protection is not required but what about standpipes? This building has three stairways. Two are interior and one is open and on the exterior. Standpipes are provided in the two interior stairways. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Anthony
2/1/2023 08:00:56 am
IF the stair is considered a required exit you'll have to provide a standpipe and hose connections. This information can be found on your G series aka life safety or code compliance documents.
Reply
Chuck R
2/1/2023 08:24:55 am
The prescriptive locations and charging language (code requirement) comes from the adopted code within the jurisdiction of the project (i.e. IBC, IFC, NFPA 1, NFPA 5000, NFPA 101).
Reply
Todd E Wyatt
2/1/2023 08:29:29 am
ANSWER
Reply
Dan Wilder
2/1/2023 08:42:34 am
There will likely be some Building/Fire code reference that will help on this because I was on the side of "If it's an exit stairwell (typically shown on the Life Safety Sheets as an egress point with occupant load) then it's required to have a standpipe"....
Reply
David Williams
2/1/2023 10:03:07 am
We have a historic building renovation job on Navy property where NAVFAC wants manual exterior dry standpipes (supervised with N2) on new exterior exit stairs, similar to what was there since the 50’s. Keeps the project from adding additional interior stairwells while providing Fire Service access to the upper floors.
Reply
Chuck R
2/1/2023 10:09:28 am
The last response quoting IBC/IFC905.4 is the correct iteration of that code section that indicates where CLASS I standpipes are to be located, but...
Reply
2/1/2023 12:35:34 pm
Recommend to contact local fire department to if having the standpipe in the open air stair would be a tactical advantage to fire ground operations. Interior stairwells can impede fire department access when both stairwells are used for exiting.
Reply