We have a 3-family building with parking garage and three floors over parking for a total of four floors.
According to the IBC, a standpipe is required; my question is - is the standpipe required in all stairs? We have two stars which are less than 30-feet between the stairs. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Pete H
8/17/2023 06:29:44 am
Check IBC (or your state's version of it) around section 905.4, 905.5, and 905.6.
Reply
Christian H
8/17/2023 08:31:10 am
To add to Pete's IBC reference. Are all the stairwells a "required interior exit stairway"?
Reply
Dan Wilder
8/17/2023 07:57:34 am
NFPA 14 - 19' 7.3.2.5 allows for a single hose connection between two "OPEN" stairs within the "OPEN" corridor.
Reply
Josh
8/17/2023 08:17:25 am
Dan, do you know if this would be applicable in a stairwell where there's a 2 hour barrier cutout with automatic closing walls if there's a fire? I hadn't thought about that until today.
Reply
Dan Wilder
8/17/2023 09:28:45 am
From a responding department perspective, breaking a rated enclosure without having an active and already available water supply would be a big red flag. If the stairwell becomes a rated enclosure during a fire, I would provide the hose valve connections within the stair rated enclosure.
Glenn Berger
8/17/2023 08:06:18 am
If the stairs are enclosed and separated then I would say the answer of providing 2 standpipes is yes. In the end, you do want to provide the FD the best approach to controlling and suppressing the fire condition.
Reply
Jesse
8/17/2023 08:08:55 am
Depending upon the layout of the stairwells, it may be possible to have standpipe risers in two of the stairwells and have a hose connection between the two. 14 spells out the parameters for this approach.
Reply
Alex
8/18/2023 04:34:49 am
To add my two cents on Josh’s sub question, when designing, I would look at the worst case scenario the fire department could arrive at. If there is a 2 hour fire wall that closes upon fire, then design with the wall closed, not open.
Reply
Brian Lane
8/23/2023 11:43:05 am
I have a tangential question relative to 905.4 provide a class I standpipe at "...each story above and below grade plane." Does this mean a standpipe connection is not needed at the ground floor? I've brought this up to numerous design/build sprinkler subs and they all say a connection is required at the ground floor. thanks