Can non-residential sprinklers be used in a NFPA 13R design?
NFPA 13R lists that residential sprinklers are permitted for use but does not list they are required to be used. My understanding is that sprinklers used in NFPA 13 for light hazard would exceed or meet sprinkler requirements within NFPA 13R On this premise, would installing a sprinkler for light hazard occupancy be exceeding NFPA 13R minimums, and thus be acceptable? We have a dry sprinkler system we are installing in a small existing dormitory built with combustible construction. We are using a NFPA 13R design approach which avoids sprinklering the attic space, with local AHJ approval. We need to have concealed sprinklers under request of the owner based on the occupancy, but there are not residential concealed dry pendent sprinklers, and the contractor is pushing to install recessed dry residential sprinklers. Thanks in advance.
8 Comments
Anthony
3/20/2023 08:04:11 am
No you cant use standard response standard heads.
Reply
Anthony
3/20/2023 08:10:54 am
Note you can get dry side wall sprinklers. but if you're using side wall sprinklers just us regular sprinklers that drain appropriately and are feed from the floor below.
Reply
Alex
3/20/2023 12:22:44 pm
If you are using a dry system because the attic isn’t heated, I would use Anthony’s approach and feed sidewalls from the floor below.
danefre
3/21/2023 02:59:09 pm
Question on that:
Reply
Jesse
3/20/2023 08:24:14 am
I'm not familiar with dry, concealed pendents. I'm curious as to the driver for the dry system. Clearly the occupiable space is conditioned space. So is it just the attic that isn't conditioned? You're not protecting the attic so you might be able to use one of the freeze protection examples in 13R.
Reply
Shawn G.
3/20/2023 08:36:26 am
You will have to meet the requirements for 13 if you are going with a dry system (NFPA 13R 2016 - 5.4.3). Just fyi, I believe there is a required 15 second water delivery time associated with that.
Reply
JI
3/20/2023 09:40:37 am
It sounds like NFPA 13-R 2019 6.2.1.3 is most applicable in this situation for using quick response sprinklers. Calculation as per 7.1.2. I am not sure why the limitation of four sprinklers within dwelling units other than to align with NFPA 13R calculation requirements or small room rules.
Reply
Pete H
3/20/2023 10:11:06 am
Reliable has a residential dry sidewall that's semi-recessed and not concealed.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |