NFPA 13 2016 Section 8.15.12 outlines requirements for Concealed Spaces Not Requiring Sprinkler Protection.
I am building a Type V-A (wood-framed) apartment complex. Are sprinklers required in wood-framed drop ceilings (soffits), below exterior cantilever walkways? Walkway construction is wood-framed, with insulation in the cavity, 5/8-inch gypsum below, and 2-1/4 inch hard rock concrete on crickets. The referenced assembly is GA FC 5420. This space will have soffit vents along the entire length. The depth varies from 6-inches to 12-inches. This project is under NFPA 13, thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Mike
9/29/2021 08:27:04 am
If the clearance is greater than 6 inches, yes. Read the 1st paragraph of Chapter 4,'16 and section 8.15 for special situations
Reply
Alex
9/29/2021 08:38:36 am
Hi Anonymous,
Reply
Jesse
9/29/2021 08:48:58 am
I would offer that you'll need to protect those areas if your governing standard is full 13.
Reply
Casey Milhorn
9/29/2021 09:40:40 am
I agree with Jesse if I'm understanding your scenario correctly. 4' or less in width should not need protection (again if I'm understanding the situation correctly).
Reply
William Crawford Jr.
9/29/2021 03:23:35 pm
Just off the top of my head......
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |