Asking as an employee of an architectural design firm - we have an outdoor performance center (A-5) with a 6,000 sf performance "platform". It is not being designated as a stage (just lighting and sound above).
This outdoor platform does have a lid/ceiling up about 50-ft with walls on three sides and open to the outdoor seating area. Would this outdoor space be exempt from sprinkler protection under building code for A-5 guidelines, or should it be treated like any overhang where products underneath might be flammable? I believe it needs protection, but have not worked on an outdoor A-5 Assembly occupancy before. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Pete H
9/14/2023 06:57:36 am
From 2020 Building code of NYS (and probably IBC):
Reply
Anthony
9/14/2023 07:40:58 am
From a practical standpoint I'm not sure you'll ever get sprinkler activation with 50'-0 distance from floor to 'ceiling' if you have a breeze that day or the wrong heads will go off. SO from an efficacy point of view not sure its worth it.
Reply
Glenn Berger
9/14/2023 08:23:42 am
Based upon the limited information given, I would say no protection required. I am assuming that there are no other permanent structures around this outdoor platform. I am also assuming that none of the spectators are located beneath the ceiling/roof assembly.
Reply
Chad
9/14/2023 08:35:17 am
Check with the AHJ... more than likely no based on what others said. Its not enclose, or practical to do so.
Reply
Todd E Wyatt
9/14/2023 12:12:20 pm
The scoping Code (e.g. 2021 IBC) determines the scoping requirements WHERE (903.2 Where Required) an automatic sprinkler system (ASPS) is required based on the building's Occupancy Classifications (OC) and/or based on "Specific Building Areas and Hazards" (e.g. 903.2.11.3 Buildings 55 Feet or More in Height). The scoping Code references applicable standards, NFPA 13, NFPA 13D, or NFPA 13R, in HOW an ASPS is to be "designed and installed" (903.3.1 Standards).
Reply
Todd E Wyatt
9/14/2023 12:13:01 pm
REFERENCES
Reply
Todd E Wyatt
9/14/2023 12:13:40 pm
REFERENCES continued ...
Conrad
9/14/2023 06:12:25 pm
This is great info Todd. From the AHJ perspective, I agree that walls on three sides should be considered enclosed. This is true for permanent structures as well as temporary.
Reply
brian peceny
9/15/2023 08:19:44 am
Thank you for the detailed response. We have the national consultant (managers of other outdoor amphitheaters) telling us they have not sprinkled at other locations. We will be meeting with the Fire Marshal next week.
Reply
SCHULMAN
9/14/2023 12:34:44 pm
Stages have requirements beyond the Fire Codes and Fire Protection Sections of the Codes mentioned thus far.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |