In the stairway, on the 2nd floor only of 4-story wood-framed condo (NFPA 13R), do we require a sprinkler on the “extended landing” ? In the attached image Blue is the sprinkler in question, red are the required sprinklers. The main floor requires coverage because it has two entrances / exits from the stairway. The upper floor has full protection of the entire area. The 3rd floor does not require protection as the 4th floor does not have a extended landing. So this only applies to the 2nd Floor.
Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
Pete H
8/31/2023 06:48:58 am
I'd protect it, as I see no omission you fit in NFPA 13R section 6.6.9, though you still might be able to do it with one residential sprinkler in the middle of the stairway. A lot of residential heads are listed for 20' x 20' spacing.
Reply
Anthony
8/31/2023 08:51:20 am
Yes a sprinkler is required under the extended landings. sprinklers also are required in the stair shaft under tred as it is combustible construction.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |