May fire sprinkler coverage for an NFPA 13 system be omitted from inside an air shower?
Are there any square footage standards that would apply, or any other "exceptions" that would allow omission? This is in a large industrial factory with hazardous materials. The inverse question would be...is sprinkler coverage required inside an air shower? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Dan Wilder
6/13/2024 07:53:31 am
NFPA 13 Section 4.1 states protection is throughout unless there are exceptions. Closets, chases, and other smaller locations require protection within, so I don't see a code-based exception for omission.
Reply
Anthony
6/13/2024 08:14:58 am
I agree with Dan, you'll need a sprinkler here. Try the 'clean room' gasket concealed sprinklers if there is a hard lid in the area. That'd keep the air/dust from leaking above the ceiling.
Reply
Glenn Berger
6/13/2024 08:16:42 am
Is your "air shower" a piece of equipment that will be installed in this facility? If its equipment, rather than a "constructed room," then an argument may be made to avoid the inclusion of sprinklers.
Reply
S
6/13/2024 09:38:42 am
I do not agree with this answer as a whole due to we had to provide coverage in 77 of 6'x8'x7' high enclosed soundproof auditing booths that were side by side spaced about 6" apart and there was coverage above. I agree it was a total waste, but I suggest speaking with the AHJ.
Reply
Jack G
6/13/2024 10:13:56 am
I m with Glenn.
Reply
Jesse
6/13/2024 10:16:40 am
Agree with Glenn here.
Reply
Todd E Wyatt
6/13/2024 11:12:28 am
The adopted scoping Code (e.g. IBC-2021) determines WHERE an automatic sprinkler system (ASPS) is required to be installed and the Reference ASPS Standard (e.g. NFPA 13-2019) prescribes HOW a building’s/structure’s ASPS is to be designed, installed, inspected, and maintained.
Reply
Pete H
6/13/2024 12:39:23 pm
Not seeing any specific exclusion, I think you have to protect it unless you can get AHJ permission to go beyond code with the omission.
Reply
Wes
6/13/2024 12:50:03 pm
Also, keep in mind that air curtains or these clean air barriers are probably the sole ingress/egress path from a clean space.
Reply