I have two above ground 20,000 gallon (US) PET storage tanks, used for food grade oil, located inside in a manufacturing facility, all above ground. I went through NFPA 30 back and forth, still couldn't find what sort of sprinkler protection do I need for this. Cooking oil is considered a Class IIIB liquid, and all references I could were about all other classes, but IIIB. The only reference to IIIB seems to be in smaller containers, in the rack, but no tank storage mentioned. How do I go about designing protection for the tanks? What about the surrounding area? Thanks in advance.
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Glenn Warga
7/10/2023 08:05:12 am
Look into FM 7-88 Table 12 and see if it applies.
Reply
Cassandra
7/10/2023 08:22:39 am
I know these are storage tanks, but we use spray mist systems for fryers in cook plants. They are extremely effective. Not an expert here, definitely a newbie to the group, but have been reading Meyer Fire for 2+ years.
Reply
Glenn Berger
7/10/2023 08:37:27 am
Are you asking about facility protection sprinkler system? Or are you asking if storage tank related sprinkler system?
Reply
Skyer
7/10/2023 09:19:25 am
Where I work with often deal with large amounts of Class IIIB liquid in the form of cooling oil. We follow NFPA 13 for Ordinary Hazards. There is no specific requirements for tank protection in the code for Class IIIB liquids.
Reply
Jesse
7/10/2023 10:42:17 am
For facility protection I think it puts you in 13 OH2. I don't see a requirement for tank protection.
Reply
Anthony
7/10/2023 11:13:17 am
I've been though this recently myself. The tanks don't require protection. The reason you can't find protection criteria in 30 is specifically because the liquid is in a tank. NFPA 30 like FM 7-29 are for smaller 'packaged' amounts of liquids in storage racks.
Reply
7/10/2023 04:42:47 pm
I agree with everyone on Class III liquids needing fire sprinkler protection. However; I would check with the AHJ and owners insurance underwriter to see if they have more restrictive requirements. Also why is there no secondary containment?
Reply
Janak Patel
7/12/2023 11:36:53 am
NFPA Chapters 21 and 22 do not specify a requirement for providing a sprinkler protection for an above ground, in a building, Combustible IIIB liquid storage tanks. However, NFPA 30, Section 21.6.1.2 and Section 21.6.3 requires performing a formal fire and explosion hazards analysis which includes the tank protection and the building protection.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |