We have a school theater project where there are three catwalks (each 3'-9" wide) above the seating area that have cloud ceilings that completely cover the bottom of the catwalk. The ceilings are within 6" below the bottom of the catwalk.
There is ceiling level sprinkler protection and sprinklers dropped into the clouds. I do not think that a line of sprinklers is needed in between the bottom of the catwalk and top of the cloud. The A/E is saying that three levels of sprinkler protection is required in this situation (ceiling, catwalk, & clouds). Is sprinkler protection required between the catwalk and ceiling below? Any help either way, for or against adding the extra line would be great. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Dan Wilder
5/18/2021 08:02:46 am
I would say 8.5.5.3.1.4 fits your example (13-16) and no additional sprinkler level is required.
Reply
Chris
5/18/2021 08:35:07 am
Per 13(16) 8.5.5.3 Sprinklers are required under continuous and non continuous obstructions. However, your catwalk of 3-9 does not meet the minimum required width of 4-0, which per 13(16) 8.5.5.3.1 Sprinklers shall be installed under fixed obstructions over 4-0 in width.
Reply
Mike
5/18/2021 08:46:03 am
Assuming they are open grating:
Reply
Jessica Lutz
5/18/2021 09:21:54 am
I concur with the previous comments. Looks like you have enough ammo to me!
Reply