I had a discussion with other peers about the hazard classification of nail salons (not a hair salon in this case).
Peer 1 argued for OH2. It's semi-mercantile, typically behind the front desk they sell beauty care products of moderate flammability. Peer 2 argued for OH1. It's not mercantile like we're used to; it's not aisles, it's a couple of cabinets by a front desk in the majority of cases. But the chemical storage in those beauty products to him says he can't go all the way light hazard even with mostly open floor space. Peer 3 argued for Light Hazard. This is no different from a doctor's office. They have cabinetry, they have equipment, they have flammable chemicals (alcohol at the very least). Plus he'd really like to be able to use CPVC pipe for the light hazard occupancy to save money. I see the argument for all three, so I figured I'd offer it to more peers. See where folks land on this. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Alex
11/6/2023 05:23:47 am
I would argue against categorizing nail salons as a light hazard category. The presence of acetone and other solvents often requires flammability permits, indicating a risk beyond what light hazard protection would cover.
Reply
Pete H
11/6/2023 06:40:22 am
I really like Alex's point about the size of the Nail Salon affecting it. So I'm going to piggy-back on that.
Reply
Glenn Berger
11/6/2023 08:12:49 am
Generically - all of the positions have merit. BUT, one needs to consider the actual application, the actual planned quantities of hazardous materials that can be stored and handled at the this facility. Also, one needs to consider the size of this facility.
Reply
Jack G
11/6/2023 08:44:05 am
If it’s in a shopping mall or strip store, I d classify it OH 2, so that the system had enough density for down the road and a new tenant.
Reply
Anthony
11/6/2023 12:03:33 pm
I agree with this logic. Especially if its a small footprint. Otherwise LH would be fine.
Reply
Jesse
11/6/2023 09:39:00 am
Agree with Glenn. All positions have some merit. I think inherently the nail salon is LH unless they're keeping large quantities of Class I Flammable Liquids like acetone. I would argue this to be incidental to the use.
Reply
Robert M
11/6/2023 09:40:01 am
I have recently fought a fire in a large nail salon/bar occupancy where the stored chemicals fed the fire and led to a complete loss of the building. This building was not sprinklered as it was an older building that changed hands many times. The flammable liquids engulphed firefighters in flames (they were storing them in an attic). I don't know if there is an option for a flammables room with greater protection than the "retail" area.
Reply
Brian Cockburn
11/6/2023 09:58:15 am
If the water supply is up to it, I would design to OH2. You'll have more protection than would likely be needed and a future retail tenant would have a working sprinkler system with little need for modification.
Reply
Anthony Brown
11/6/2023 12:14:31 pm
I have done a number of Nail Salons and all but one was OH1 and accepted by the AHJ. The only hold out was OH2 and that was because the back store room also served as a storage area for two other Salons and some of the very flammable items were in one and five gallon containers stored in a locker.
Reply
sean
12/31/2023 11:20:00 pm
light hazard anytime, unless they lave bulk storage or combustible liquids
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |