I have a distillery with H-3 occupancy. They will have one (1) stainless steel 100 gallon tank (never full) of 65% alcohol for distilling whiskey.
They plan to have maximum 6-ft storage of approximately 25-gallons maximum of finished product in bottles on shelves. Also planned is approximately thirty (30) 30-gallon wood barrels stacked (2) high in adjacent areas I am seeing a lot of exceptions in IBC and IFC for the wooden barrels with the H-3 Occupancy. Can you provide any insight to this allowance for wood barrels and how I might determine the proper sprinkler density and maximum volume (if any with the H-3)? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Jesse
12/30/2021 08:47:05 am
My 2-cents.
Reply
Joshua Freedman
12/30/2021 11:57:09 am
I’ll throw in my 2 cents that as an inspector, I often see installations that used some exception found in IBC or local code but if this contradicts what is required per NFPA, it is often unacceptable. If any exceptions are being sought out or corners cut for cost savings, I would inform the customer of the possible savings, but also advise that their insurance provider, or even the City down the road might not accept it (which I have seen occur). As such, I always strongly recommend designs be to NFPA or FM standards which need to consider not just sprinkler design but possibly other things like damming or other secondary containment, grounding, deflagration controls, Class I, Division 2 electrical, etc – the whole of the code must be applied. I have rejected set ups that were designed properly in so far as the fire sprinkler system was concerned but there were no deflagration controls in place.
Reply
sean
12/31/2021 06:15:36 pm
you also need to keep in mind what version of the IFC/NFPA you are using as there was a big reclassification in the recent years
Reply
Ron
1/5/2022 12:59:30 pm
Not sure where you are located.... I had a project in Kentucky a while back. Apparently distilleries are a Thing in Kentucky because I noticed a lot of direction regarding fire protection for alcohol and whiskey barrel storage in the Kentucky state codes while reviewing the local requirements. Check your local codes too.
Reply
Eric
1/5/2022 01:27:36 pm
it seems there are many gray areas with this type of design. I do not see clear density requirements anywhere I have looked. wood barrels will be stacked on the floor and only 2 high for a total of 30 barrels at the max storage. up to 25 gallons of final product will be stored on shelves in bottles.