Topic: Water Delivery Time in Single Interlock Preaction Systems Question:
I'm currently designing a single-interlock preaction system and I'm seeking clarification about the water delivery time requirements under NFPA 13 (2013). Section 7.3.2.2 mentions that the system size cannot exceed 1,000 automatic sprinklers but doesn't specify the water delivery time for single interlock systems. On the other hand, Section 7.3.2.3 clearly states that double interlock preaction systems must deliver water within no more than 60 seconds. Does this mean that single interlock systems are not required to adhere to a specific timeframe for water delivery? In my view, it makes sense to not include a delivery time for single interlock systems, since water should already be at the sprinkler prior to activation. I'm interested in others' views or experiences in this area. Thanks in advance! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Dan Wilder
1/19/2024 07:24:30 am
You are correct, no water delivery time requirements for a single interlock. In the later 2022 edition, the enhanced content explains why:
Reply
Jesse
1/19/2024 09:04:37 am
Yep what Dan said. These will operate in a time similar to a wet system.
Reply
Franck
1/19/2024 10:56:19 am
Double interlock is considered as a dry pipe system with same restrictions (time, increase of designed area) while a single interlock is considered as a wet system for the reasons mentioned by Dan.
Reply
Dave
1/19/2024 11:04:25 am
When it comes to preaction systems, I often have to explain to clients, "double" is not automatically better than "single," there is a time and place for each. Especially if it is an FM Global project.
Reply
Glenn Berger
1/19/2024 11:54:40 am
Franck response is spot on.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |