Can sidewall heads be used for water curtain application?
While typically pendent are used to provide a water curtain around a vertical opening, I am working on a project where the arrangement led to sidewall heads being preferred by the architect. NFPA 13 is not explicit about water curtain needing to be a specific type of sprinkler, it just says it should be a standard spray with 3gpm /lineal ft applied. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Pete H
12/29/2022 08:04:49 am
I see no code reason why not as long as you don't have any gaps in coverage or have any sprinklers too close without baffles.
Reply
Jesse
12/29/2022 08:12:10 am
Architects....
Reply
Glenn Berger
12/29/2022 08:16:28 am
IMO, it depends on your specific application. Your application is a curtain system around a floor opening, I would use pendent sprinklers in this application. There are published limitations where vertical sidewall sprinklers can be used.
Reply
Todd E Wyatt
12/29/2022 09:27:08 am
SUMMARY
Reply
Todd E Wyatt
12/29/2022 09:28:19 am
REFERENCES (Part 2)
Reply
Jay
12/29/2022 03:52:05 pm
Todd, please see the section you referenced above, 712.1.3 Escalator Openings for the requirement of closely spaced sprinklers with draft stops, aka water curtain sprinklers.
Jay
12/29/2022 05:07:51 pm
Also, the code does not require the "window" sprinklers used for atrium enclosure, in lieu of 1-hr fire resistant glazing, to be a deluge sprinkler system.
Todd E Wyatt
12/30/2022 07:10:21 am
The commentor did not state that the Vertical Opening (VO) was an esculator opening. If it is, it would be required to meet the prescriptive requirements of 712.1.3 Escalator Openings :
Todd E Wyatt
12/30/2022 07:15:23 am
"Also, the code does not require the "window" sprinklers used for atrium enclosure, in lieu of 1-hr fire resistant glazing, to be a deluge sprinkler system."
Anthony
1/2/2023 11:26:04 am
First off you can only use closely spaced sprinklers for: atrium protection or if you have a letter from the AHJ saying that sprinklers that are closely spaced are an approved alternative.
Reply
Aidan Bird
10/11/2023 01:41:28 pm
In the case of the protected opening exception, 705.8.2 (Seattle Building Code, 2018) sprinkler system with heads designed for water curtain can be used. Is this a deluge system? Or area the heads just added along the area of windows that need protection... ?
Reply
Moderator
10/13/2023 01:41:37 pm
Hi Aidan,
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |