We have a series of highrise buildings where an NFPA 13 sprinkler system and a wet standpipe system (NFPA 14) are to be installed.
If the sprinkler and the standpipe systems are supplied by a common fire pump, and horizontal supply pipe, but have separate vertical risers, will the system be considered a combined system? Will the subsection of NFPA 14 (2019 Edition) section 7.10.1.3.1.1 apply? 7.10.1.3.1.1 In a building protected in accordance with NFPA 13 or NFPA 13R, the water supply for the combined sprinkler and automatic standpipe system shall be based on the sprinkler system demand (including any hose stream demand) or the standpipe demand, whichever is greater. The buildings are fully-sprinklered, and the proposed fire pump is rated at 1,000 gpm. There is a water storage tank of 30,000 gallons. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
schulman
5/11/2022 08:12:41 am
yes.
Reply
Jesse
5/11/2022 08:24:58 am
Yes indeed, its combined system and yep NFPA 14 7.10.1.3.1.1 applies.
Reply
Glenn Berger
5/11/2022 08:29:28 am
You have a combined system.
Reply
Dan Wilder
5/11/2022 08:35:56 am
Lots of info so lets take some bite size answers...
Reply
OP
5/12/2022 02:04:29 am
Hi Dan,
Reply
Alex
5/11/2022 08:48:46 am
Hi,
Reply
Todd E Wyatt
5/11/2022 09:00:28 am
Regarding the discussion of "podium" buildings ... 2021 IBC Section 510 Special Provisions describes (8) conditions that exempt or modify the allowable building heights and areas based on the Occupancy Classification (OC) and the Type of Construction (TC).
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |