I have a project which includes two 6-level buildings (a parking garage and a residential structure).
The garage is reinforced concrete and cold. The residential portion right next to it (8 inches away) is mostly wood construction and warm. The project has a seismic design category of B - so no earthquake bracing throughout. Because the garage is cold, I have the dry control valve on a combination standpipe in a warm closet in the residential portion. The 3" feed then travels across the 8" gap to the garage. This happens at all 6 levels. My question is, do I need a seismic separation assembly on one side or the other at each of the levels where the dry feed travels across the gap? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Glenn Berger
1/17/2022 08:11:39 am
Are you passing through two separate walls? Is there fire-rated construction between the two facilities?
Reply
Kallmeyer
1/17/2022 08:27:32 am
We are passing through two separate walls. There is fire-rated construction. Nowhere in the arch or struct plans does it call this "gap" a seismic separation.
Reply
Dan Wilder
1/17/2022 08:24:52 am
What do the structural plans/details call out for this gap?
Reply
Brian Gerdwagen FPE
1/17/2022 08:25:43 am
What you have is a building expansion joint that will need some flexibility in the piping to accommodate the movement of the building due to settling or thermal changes.
Reply
SCHULMAN
1/17/2022 08:57:42 am
rated separation expansion joints are designed so that one or the other structure could fail catastrophically without taking the other structure with it ... the flexible "break-away" couplings on the piping will save one side of your fire protection system in the same way.
Reply
RJ
1/17/2022 09:26:24 am
Can you feed the garage just once at the bottom, then have a dry standpipe feeding only the garage? With this, you would only have 1 area feeding the garage.
Reply
Alex
1/17/2022 08:13:51 pm
Hi,
Reply
Pete D.
1/17/2022 07:53:00 pm
This is off topic from the question you asked, but depending on the temp difference between the two zones, you may have a problem with moisture condensing on the warm side of the thermal zone barrier. I would insulate 12" into the warm zone and 3-6 ft into the cold zone, depending on delta T.
Reply
Anthony
1/18/2022 07:37:46 am
A lot of comments on if you HAVE to but id suggest you SHOULD. Buildings move and settle if you're not designing for the future are you really designing at all?
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |