Does a security grill utilized in school corridors required to be tied into the fire alarm?
If so, the concept should be that the grill in the closed position should return to the open position when fire alarm is activated, correct? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Glenn Berger
5/13/2024 08:14:54 am
The easy answer to this question would be yes. However, the right answer would be dependent on the school's emergency operation procedures. Construction type and layout would also play a factor.
Reply
Todd E Wyatt
5/13/2024 08:16:22 am
Security grilles (SG) are permitted in the Means of Egress (ME) per the scoping Code (IBC-2021) but are limited to 50% of the Exit Access doorways and/or Exit doorways. SG are permitted at the main exits in Group B, F, M and S Occupancy Classifications (OC) but not at Group E Education OC.
Reply
Todd E Wyatt
5/13/2024 08:23:08 am
Additional info from NFPA 72 National Fire Alarm and Signaling Code :
Reply
Ricardo Gonzales Jr
5/13/2024 08:17:57 am
It depends. What is the Security Grill for? Does it affect egress or not. The Architect or Life Safety Engineer should be able define that for you. As a Fire Alarm designer, you should ask the questions and get them to provide the answer. It's their job to know egress and it's a CYA for you. Documented from the Architect or Engineer.
Reply
Chad
5/13/2024 10:10:24 am
What Ricardo said, 100%
Reply
Steve Cooper
5/13/2024 09:40:36 am
I believe you would want all security features tied together. It could be wired or arranged separately depending on how the schools set up their emergencies.
Reply
Jack G
5/13/2024 09:43:48 am
I believe that the school districts liability comes into play and that they should open in the flow of the egress routes