Hi all - I am currently reviewing an ESFR sprinkler protection of compressed, rolled-mattresses in cartons.
During a fire, once the carton burns, the mattresses will be able to retrieve, at least partially, its initial uncompressed configuration. Considering this, I'm skeptical about it being classified as a cartoned unexpanded plastic. It seems to me that the proper classification should be cartoned expanded plastics, as I've found nothing justifying this optimistic opinion. Do you have an opinion on how this should be properly classified, or how you would view it? I'd love to hear about your point of view on the subject and choices made for similar projects. Thanks and regards. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Pete H
5/1/2023 06:40:27 am
Ultimately it depends which type of foam is used to make your mattress.
Reply
Pete H
5/1/2023 06:42:39 am
Also worth noting in Table A.5.6.4.1 (NFPA 13 2016 edition) is that "Mattress; foam (in finished form)" is also noted as an Expanded plastic.
Reply
Dan Wilder
5/1/2023 07:09:49 am
I'm with Pete...
Reply
Anthony
5/1/2023 07:30:35 am
As you said, and I agree:
Reply
Jesse
5/1/2023 08:06:19 am
I agree with the others. I'd definitely treat this as cartoned / expanded.
Reply
Jesse
5/1/2023 08:08:58 am
I hit submit too fast.
Reply
Franck
5/1/2023 12:45:44 pm
You can compress it as much as you want, an expanded plastic remains an expanded plastic (mainly because of its chemical characteristics, not only because of the possible amount of air trapped).
Reply
Bjørn B
5/1/2023 02:51:18 pm
I agree with the others. When you have a fire it will quickly become exposed expanded,
Reply