A resident in our area is planning to install ground-mounted solar for an existing home, along with storing the energy produced in batteries. The area for the batteries (ESS - Energy Storage Systems) is a storage room which is accessible only through the inside of their garage.
Would this storage area still be considered a "living area" and thus subject to the max 20kWh of ESS per the IFC section 1207.1.1 (table)? Or, could they store more batteries in this area since it's only accessible via the garage area?
9 Comments
Franck Orset
5/31/2024 08:25:05 am
I will leave the floor to other peers regarding legislation in the US.
Reply
Joe
5/31/2024 08:40:47 am
Not sure what edition of the IFC you are using but most AHJ are using the most current edition 2024 for ESS since the rules, regulation and technology is every changing.
Reply
joe
5/31/2024 08:53:52 am
sorry for the typo is read
Reply
Jesse
5/31/2024 08:42:53 am
Great answer by Franck re: the reduced, but not eliminated, threat of thermal runaway with lithium iron phosphate ion batts.
Reply
Chad
5/31/2024 09:06:33 am
From an AHJ perspective, trying not to piss off a single family home owner, or the green movement folks:
Reply
Joe
5/31/2024 09:15:28 am
Does the IRC reference this IFC section? How do you get to IFC on a single-family detached dwelling?
Reply
Ricardo Gonzales Jr
5/31/2024 10:04:42 am
Note 1st that the IFC doesn't affect Residential Homes. Then comes in the question of IF the Jurisdiction has adopted NFPA 855. Most have not.
Reply
Joe
5/31/2024 10:41:42 am
Please review IFC 2024 edition section102.5 and section 1207.1.
Reply
Joe
5/31/2024 06:43:34 pm
Agreed but this is an R-5 Leave a Reply. |