I have an existing, single-story building. It's existing Ordinary Hazard Group II that is going to change from acoustical ceiling tile throughout to have no ceiling and be open to structure. The space will essentially be wide open (like a furniture store).
The existing automatic sprinkler system has a 4 inch main that runs the length of the building with branch pipe for the sprinklers. Would it make more sense to remove and replace the branch pipe for the open structure layout with upright sprinklers, or keep the branch pipe and armover as needed for upright sprinkler spacing? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Alex
4/15/2022 06:09:54 am
Hi,
Reply
Michael
4/15/2022 08:07:08 am
I would think the existing piping would be too low for the new open ceiling concept.
Reply
Jesse
4/15/2022 08:10:32 am
Lot of variable here. What was the occupancy hazard class prior? Will there be "storage" of furniture, or just a showroom?
Reply
Glenn Berger
4/15/2022 08:30:02 am
Ask three different sprinkler contractors and you will get three answers.
Reply
Hunter
4/15/2022 10:18:43 am
How many heads we talking plus or minus what?
Reply
Scott McBride
4/15/2022 11:57:11 am
It will depend on the ceiling/roof to deflector distance of the exiting sprinklers. If the drop ceiling is a greater distance that what is rated then they will have to take a look at the design of the system. Either way I would have a Sprinkler Company or Fire Protection Consultant take a look at it.
Reply
Pete H
4/15/2022 12:38:46 pm
Depends how long your sprigs for the uprights will be, how close the branches are to the new upright locations, is your hazard going to change? And of course.... after they remove all the ceilings, is there a plan to make this a storage facility? In which case, this may have to be redesigned for storage.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop June '24 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
July 2024
PE PREP SERIES |